Hi all i have a problem on a kitchen ring that has been reconnected by a different firm on a complete rewire. The building has been rewired apart from a kitchen that was joined onto existing wiring. Problem is, one I don't have a ring and two, I get power but then it goes off after an hour or...
Hi All,
Just purchased the mft1741+it seems good but my old mft 1721, when doing a ZE or ZS reading it would start automatically and stop once the test was complete. Ive got the new one to start automatically now, but when it brings up the result it keeps measuring and i have to press the test...
I am currently doing an EICR in a warehouse and one of the circuits is for a Fork Lift Charging point (32A) In Light of the 18th Edition and all circuits being protected by and RCD, should I recommend that the MCB that is feeding that circuit at present be changed to an RCBO ??
Hi All
I have just done a board change at a house that i'm sure is a TT System. (The House is supplied by overhead cable to the house with an earth rod net to where the external meter is fitted).
Once I had changed the board, I did a ZE Reading and GOt 5.63 Ohms. When testing the 30mA RCDs on...
Hi
I have just changed both an off-peak CU and a normal CU. I have tested both. Can i put them both on the same cert or do they need to be on two different EIC's ??
I have had a look at my regs book, and as far as I can interpret that if it is inside a cupboard thus providing a partition and with the electrical connections being outside of the bathroom, I cant see a problem. Am I missing something?? just want to be sure.
Hi All, Just a quick question, my decorator wants to put his washing machine in his bathroom as it is the only place they can put it where it can be plumbed in easily. It will sit under his boiler which is also in the bathroom and both will then have a cupboard built round them. He tells me...
Actually I will ring Knightsbridge in the new year but no idea as to the LEDs, will have to try and find out I suspect bought separately as a kit would have probably worked correctly.
To be honest I was just there to exchange a Fan for them and they asked me to take a look as an after thought asthey have never worked since being fitted, so I took a couple of pics and thought i would ask on here in case this is a common easy fixed fault. I have read some of the previous posts...