Recent content by rigby

  1. R

    Home charger points for electric cars, anyone else done them??

    Yes I installed dedicated 32A radial circuit 4mm T and E partly in conduit outside weatherproof unswitched 13A double socket 45A isolator switch in meter cupboard.
  2. R

    High ZE Reading in Flat

    Have you nulled your leads resistance before testing?
  3. R

    Ring and Spur

    Thank you all, Method A makes life easier to lay out the spurs in the kitchen area.
  4. R

    Ring and Spur

    Hi, which arrangement is the correct one for Fuse Spur on a ring circuit?
  5. Ring spur question1.jpg

    Ring spur question1.jpg

  6. Ring circuit question 2.jpg

    Ring circuit question 2.jpg

  7. R

    Electric shower rcd consumer unit connection

    Thank you Kingeri and handysparks, I thought of Henley blocks but there is no space at all anywhere, its boxed in old iron made fuse box /meter , I was wondering if there is anything that can be used to connect on the busbar itself? as there are two spare spaces but no way to connect the R1...
  8. R

    Electric shower rcd consumer unit connection

    New one way rcd protected cu to be installed but the old fuse box (no rcd) main switch does not have space for the R1 wire that is to be connected though the Rn an R2 can be easily connected in the old fuse box, the busbar itself has couple of unused spaces but I can not find any MCBs that will...
  9. R

    Lighting Circuit Zs

    Thank you wirepuller, this clarifies the concept clearly.
  10. R

    Lighting Circuit Zs

    Low batteries!! yes I do have low batteries, I wonder if this is the reason. I shoulds change batteries and see. Thanks dwardy
  11. R

    Lighting Circuit Zs

    I must be confused about some wording, Light circuit R1+R2 is 1.84 Ze measured = 0.28 So if I do Ze +(R1+R2) I get 2.06 Maximum Zs allowed is 6.14 actual measured Zs is 0.88 This measured Zs is much lower than the max value, I know higher is not good but lower Zs leads to any problems ??
  12. R

    Joints in ring circuit

    Hi Engineer54, I dont know how it was originally, all I know is that they had one ring circuit for upstairs-downstairs alltogether and it was split into two few years ago. I think its all there apart from the accessible bit- I am going to treat them as safe they are all labeled above floor...
  13. R

    Joints in ring circuit

    Guitarist and telectrix, so far I have not tested anything just visual. will let you know when the fun begins ...
  14. R

    Joints in ring circuit

    Sockets were not moved at all, I was told that its done (2006-07 ish) to split one ring into two rings, up and down stairs plus some additional sockets downstairs.
  15. R

    Joints in ring circuit

    Thanks again truckster, I will advice for maintenance free replacement.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock