Recent content by Risteard

  1. Risteard

    UK Earth bonding to Water

    In my opinion the periodic inspection was around half of the price that it should have been. What this suggests about the competence of the Inspector is up to you to decide.
  2. Risteard

    Cable sizing earthing conductor

    What size is the supply (in kVA)?
  3. Risteard

    EV charger issue - Garo PME trips

    Also the EVSE must not be on a shared RCD which it is.
  4. Risteard

    Pulling live meter tails from isolater switch in consumer unit

    It's not simply a matter of it being unreasonable in all of the circumstances to work dead, it additionally must be reasonable to work at or near it live, and also suitable precautions must be taken. No point in only quoting one of the three absolute requirements in the law for live working.
  5. Risteard

    EV charger installation

    If they want it at a minimum of 600mm depth then that is what you need to do. Anyone else's opinions aren't relevant.
  6. Risteard

    7. 3 kw INDUCTION HOB

    Surely it's a three-phase supply there rather than a large single phase supply? You really need someone familiar with Czech wiring regulations and practices.
  7. Risteard

    SuperRod magnetic R1R2 leads

    I have a set. I must admit that I seldom use them however. But the concept is good in my opinion.
  8. Risteard

    Regulations around stairwell wiring

    I would ask the fire alarm installer to justify his claim. That said, personally I think that metallic containment would be a better solution for all of the reasons mentioned in response to your post. But that's not to suggest that non-metallic containment would be in breach of any Rule.
  9. Risteard

    EV charger installation

    Sounds very cheap for that to me. Certainly I would charge more for that. I would have expected data cable at least for load curtailment purposes however.
  10. Risteard

    EV charger installation

    In the old days of the OLEV grant we used to have to send proof of manufacturers' approval for each different make & model of chargepoint we could fit under the grant. Of course each manufacturer insisted on doing their training first...
  11. Risteard

    New T&E cable...

    Indeed. And in more recent years it must also be certified Dca, -s2, d2, a2 or higher. (Essentially LS0H.)
  12. Risteard

    New T&E cable...

    Furthermore a representative of Doncaster Cables themselves has also stated that it is not rated as insulation, but is merely there as identification as you state.
  13. Risteard

    2 x Main Switches in on consumer unit

    The actual main switch must isolate everything.
  14. Risteard

    UK 32A or 40A breaker for 7kW EV Charger

    Yes, and in my opinion strictly speaking does not comply with BS 7671 as the RCD-style functionality of the device is not actually achieved by the presence of an RCD complying with one of the listed Standards.
  15. Risteard

    UK 32A or 40A breaker for 7kW EV Charger

    OK, when you refer to the RCD within the unit deriving from an RDC-DD (not RCD-DD) within the unit, then I am surmising that this is an electronic device within the unit and not actually an RCD complying with BS EN 61008 or BS EN 61009. As such, personally I do not feel that it is compliant to...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock