Recent content by sparkol

  1. S

    why has house got two meters?

    Because the customer’s paying two standing charges and has to deal with separate electricity bills
  2. S

    why has house got two meters?

    Thanks for all the replies. I’ll speak to DNO as telectrix says. Jut annoying that I only get chance to look at these things on Saturdaywhen they’re shut!
  3. S

    why has house got two meters?

    Nope, couple of ring mains, but I’d be interested to know what you're thinking - old storage heater circuits?
  4. S

    why has house got two meters?

    Not really Murdoch due to the way the circuits are splitbetween boards. Mostly sockets on one,mostly lights on the other.
  5. S

    why has house got two meters?

    Been to look at a fuseboard upgrade. The house has a 3-phase cutout. One phase isn’t used, and the other two phases feed a single phase meter each. The house therefore has two single phase meters, each feeding an old wooden Wylex board. One meter/board does lights, garage and a few...
  6. S

    Faulty light switch causes shower pump to start up

    Dillb - I find the majority of faults tend to be resolvable within an hour, but a few can take much longer. When I have 2-3 weeks’ of work booked in ahead of me, and an employee who I have to pay whether we are working or not, then the practicalities of the job mean I can’t just leave a clear...
  7. S

    Faulty light switch causes shower pump to start up

    I used the time I had available to ascertain that the switch was faulty, megger the circuit LN to E and look at the wiring in the loft. I couldn’t replace the pull-switch as I didn’t have one in the van. Rather than charge the customer for an hour’s worth of testing, leave him with a faulty...
  8. S

    Faulty light switch causes shower pump to start up

    252 mega-ohms on LN to E. Didn't do an R1 R2 (yet).
  9. S

    Faulty light switch causes shower pump to start up

    Went to look at a job where the customer was complaining of his bathroom lights working intermittently and also that sometimes he was hearing ‘a loud noise like thunder’ when he turned his bathroom lights on. Found that the connection in the light switch was ropey, and when the switch is...
  10. S

    Replacing a 3 phase oven

    Great stuff, thanks
  11. S

    Replacing a 3 phase oven

    Yes I've found the manual and indeed it looks like a straight swap. I know this was a slightly weird post but I'm just trying to be cautious because its outside my comfort zone. The manual says nothing about which phase does what. Is there any danger involved in interchanging phases or does it...
  12. S

    Replacing a 3 phase oven

    Thanks, will do. But what I need to know now, at this point in time, is that IF I agree to swap this oven can I be fairly confident it will be five wires out and five wires in, and I won't get stuck and leave the customer with no oven? I'm sure you can see where I'm coming from.
  13. S

    Replacing a 3 phase oven

    Hi. I’m a spark with plentyof experience of domestic single phase but not much commercial, and 3 phase isjust a distant memory from college. I have a customer who wants a 3-phase oven replacing. It’s on a suitable circuit with all-poleisolator so it should just be a simple like-for-like swap...
  14. S

    Small domestic business drowning in admin

    Hi all I do mostly domestic work, tiny jobs to rewires. I'm inundated with work and desperately need to reduce the time I spend on admin so I can spend more time keeping up with demand. I was wondering how other people deal with quotes, invoices, certificates, notifications, etc. I currently...
  15. S

    No 'HW off wire' - why not?

    Yes, this timer has a setting for gravity-fed systems, which it says does not allow indepedent setting of heating without hot water. So, I can put the timer on this setting and just transpose the wires?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock