Recent content by yellowvanman

  1. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    That I think clinches my dilemma - C2 it is!
  2. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    I know I shouldn't be worrying about a solution, but the easiest way to resolve is to put the immersion on the ring! I do realise that its not recommended (not prohibited though) but as its not used much (if at all) I think this should be OK.
  3. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    I'm not, but I can't assume anything either way. I was already to make it a C2 until the software I used highlighted that 1mm T&E using Ref C was ok!
  4. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    For your information 1.0mm T&E with Reference Method C is 16A
  5. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    Doing an EICR, one circuit described as Central Heating with 1 mm T&E cable connected but on a 16A MCB. When I look closer it appears an Immersion heater has been tagged onto the circuit! I've not been able to ascertain the cable route and its installation method. This is a single storey...
  6. yellowvanman

    How is Solar PV saving me money?

    check your clampmeters are installed correctly
  7. yellowvanman

    Fluke 1664 FC IR questions

    Yes it can be disabled. Still getting to grips with mine so unable to comment further.
  8. yellowvanman

    Inverter on earth stake?

    Main CU is in the garage as well!
  9. yellowvanman

    Inverter on earth stake?

    Yes, sure its just the inverter, clearly shown in the schematic as well. As you I thought it may have been for the array at first. Inverter is in garage, connected via a 'Garage CU'.
  10. yellowvanman

    Inverter on earth stake?

    Been asked to replace an old consumer unit, PV installed so bonding etc up to scratch. House supply is TNCS, however with the PV wiring the inverter (Fronius) is on its own earth stake! So that makes 2 earthing systems in close proximity! Why would they want to earth stake the inverter?
  11. yellowvanman

    Alarm sounds when deactivated

    Don't normally deal with alarms but a customer has asked me for advice and consequently I come here! Old system (circ 1980s) occasionally alarm goes off during the day when its been de-activated, type in their code and it stops and everything OK until the next time. Happening more regularly...
  12. yellowvanman

    Shower isolator

    I don't want the forum to instruct me in anything I've just told you want I'm going to do, but I know others will disagree and thats their perogative. As for experience and qualifications I probably have more than you! I'm now leaving this thread with no further input!
  13. yellowvanman

    Shower isolator

    I just thought I'd let you guys mull that over! I'm sure there will be different opionions out there! Ok, I'll start with my take. Plenty of C3's, lack of RCD protection on bathroom circuits (light + heater), no RCD protection for concealed cables, no RCD protection on sockets. The only...
  14. yellowvanman

    Shower isolator

    Not sure what you guys want me to add. I've said what I will probably do in post #10. Didn't quite manage to complete all tests yesterday so have to return one day next week, which gives me time to ponder some more! Will probably include it in the observations but without a code. That way...
  15. yellowvanman

    Shower isolator

    You're now questioning my experience and you don't even know me! As I've mentioned before I like to see an local isolator for a shower but there isn't a reg to say it does not comply. But I will mention it in my EICR but won't categorise it. So if you put it down as a C3 how are you going to...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock