Discuss EICR on DB fed from generator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
12
I'm carrying out some inspection and testing this morning. I've come across something new to me. I'm a workshop they have a 3 phase DB which is ONLY supplied from a generator. The site only had a single phase supply and therefore when they need to use 3 phase equipment they simply switch on the genny to do so. Are there any precautions I need to consider before testing? All the dead tests can be carried out as normal but when it comes to the live tests im thinking there could be problems. Earthing system? High Ze readings?
 
My thought is to understand the design before attempting tests : how is it isolated, what interlocks are present, earthing and bonding design etc. What Reg book was it designed to, are there any previous tests or docs etc (might be a few blank looks :) )
 
My thought is to understand the design before attempting tests : how is it isolated, what interlocks are present, earthing and bonding design etc. What Reg book was it designed to, are there any previous tests or docs etc (might be a few blank looks :) )
There are no interlocks , it's a completely isolated system. No crash points with mains supply etc. Haven't seen a system like this before....
 
It would be worth knowing if there are any parts of the installation where the earthing for the DNO;s single phase supply,can or is linked to the earthing arrangements for the generator supplied section.
It can be surprising how these can interact.
 

Reply to EICR on DB fed from generator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
804
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
801
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
567
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
599

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock