Search the forum,

Discuss 13A BS1363 socket-outlets on a 40A MCB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
22
Hi. I found a radial power circuit on an EICR yesterday wired in 6mm2 flat twin PVC cable and have some concerns. I know that the MCB is designed to protect the cable but what about the terminals of the sockets? 13A socket-outlets are rated to 20A max and I am not sure they are designed to have 2 x 6mm2 conductors in the terminals? I thought they were designed for 3 x 2.5mm2?
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks
 
The 20A limit (I think) you mention is for the load on a double socket, not the through-current on the terminals.

The basic principle behind 13A plugs and sockets is they have the protective fuse, so it does not matter (within reason) what the supply is, so long as the supply cable is protected. After all cooker switch/outlets often have up to 45A MCB feeds.
 

Reply to 13A BS1363 socket-outlets on a 40A MCB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
628
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
914
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock