Hi. I found a radial power circuit on an EICR yesterday wired in 6mm2 flat twin PVC cable and have some concerns. I know that the MCB is designed to protect the cable but what about the terminals of the sockets? 13A socket-outlets are rated to 20A max and I am not sure they are designed to have 2 x 6mm2 conductors in the terminals? I thought they were designed for 3 x 2.5mm2?
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks