Search the forum,

Discuss 2 module enclosure in the UK Electrical Forum area at ElectriciansForums.net

Yes, you could use something like this:
https://www.NoLinkingToThis/p/wylex-ese2-ip40-2-module-unpopulated-din-enclosure/32311
But you would need to allow for earthing the metalwork (no idea if it has a terminal strip inside or not) and you could use Wago for joining the neutrals. Not ideal, but if that is all the space you have...

The preference for a bus-bar comes from a number of factors, reliability is one, the other is most MCB can only take 25mm total conductor, so you could not loop in and out cable for 100A as needed in a CU. But reliability/safety from a good connection is reason #1
 
The cable for the kitchen underfloor heating is already in and very difficult to replace it is only 0.75 T&E so cant just swap the B6 MCB for a higher rating.

That's going to be a problem then as that's non-compliant with the regulations, and if you disconnect it and reconnect to a new CU then you need to correct such a significant non compliance.
 
Yes, you could use something like this:
https://www.NoLinkingToThis/p/wylex-ese2-ip40-2-module-unpopulated-din-enclosure/32311
But you would need to allow for earthing the metalwork (no idea if it has a terminal strip inside or not) and you could use Wago for joining the neutrals. Not ideal, but if that is all the space you have...

The preference for a bus-bar comes from a number of factors, reliability is one, the other is most MCB can only take 25mm total conductor, so you could not loop in and out cable for 100A as needed in a CU. But reliability/safety from a good connection is reason #1

I see what you are saying,

Yes I was thinking the same wago for the neutrals.

That makes sense about busbar vs cable loops, although just has a thought which maybe is better is to take 2 bits of T&E from the B10 MCB inside the c/u so each MCB in the enclosure is feed from a separate cable

The enclosure you sent me is a plastic one, the metal version of the same thing has an earth terminal inside. Would I be able to use the plastic one, as is it only C/U that have to be metal ??
[automerge]1587503253[/automerge]
That's going to be a problem then as that's non-compliant with the regulations, and if you disconnect it and reconnect to a new CU then you need to correct such a significant non compliance.

I see what your saying, as in the cable is non-compliant, I will have to get confirmation on what is there
 
That's going to be a problem then as that's non-compliant with the regulations, and if you disconnect it and reconnect to a new CU then you need to correct such a significant non compliance.
Yes, well spotted if it is going in to the CU like that as regs have 1.5mm minimum for power.

Quick and dirty would be to put a double 13A socket on that heater breaker (upgraded to 16A) then you would be OK to connect 0.75mm round cable to it via a plug and 5A fuse, etc., and other heater on the other plug.
 
No offence but it looks like to me you do not have the competence to be undertaking these works.

Fair enough, as i have said i work doing temporary power systems so understand the fundimentals but not the nitty gritty of the regs when it comes to domestic, as even though they are both under bs7671 our bit bs7909 is a little different in terms of cable and distribution units

I may not be doing the work, and at the min we are just talking about the options and I am getting information over the phone

I was mainly asking if having 2 MCBs in an enclosure next to c/u would be within the regs. or does it have to be a sub c/u (like the BG one on this tread)

I will have to ask him about the cable, as it is possible he has given me the wrong information or there was a misunderstanding
 
The enclosure you sent me is a plastic one, the metal version of the same thing has an earth terminal inside. Would I be able to use the plastic one, as is it only C/U that have to be metal ??
[automerge]1587503253[/automerge]


I see what your saying, as in the cable is non-compliant, I will have to get confirmation on what is there

Yes it does have to be metal, there's no way you could suggest that is not similar equipment to a CU.

I'm not sure you do see what I'm saying.

These questions are becoming increasingly concerning that you don't have sufficient knowledge or experience to be doing these works.
 
The enclosure you sent me is a plastic one, the metal version of the same thing has an earth terminal inside. Would I be able to use the plastic one, as is it only C/U that have to be metal ??

Ah, had not noticed. Would explain why it is so cheap! Here is the metal version and it says it has an earth bar:
https://www.NoLinkingToThis/p/wylex-esm6-ip40-2-module-unpopulated-din-enclosure/666gx

Edit: I see you already know it!
 
Fair enough, as i have said i work doing temporary power systems so understand the fundimentals but not the nitty gritty of the regs when it comes to domestic, as even though they are both under bs7671 our bit bs7909 is a little different in terms of cable and distribution units

I do both electrical installation work and temporary systems under BS7909 and the two jobs are world's apart.
 

Reply to 2 module enclosure in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock