- Reaction score
- 8,876
We ran into this question on another thread. A couple of people I respect a lot have suggested it's ok. I'd always believed it wasn't ok.
I'm sure it's actually safe, but does the letter of the regs allow it?
It does actually specifically say "protected by a 30A or 32A protective device" in the reg, and says "Such circuits are deemed to meet the requirements of 433.1.1 if the CCC of the cable is not less than 20A". Given that method 103 problems with RFC's are commonly spoken of I'd always assumed that the 20A was "as installed" not "in free air".
So is 2.5 sq mm T+E installed to method 103 hooked up to a 20A OCPD arranged as an RFC allowed?
And is any installation method with a 20A OCPD arranged as an RFC allowed?
Discuss! And let's keep this civil - it's Christmas!
I'm sure it's actually safe, but does the letter of the regs allow it?
That's the only reg I know of for an RFC too.The only regulation that I know of specific to the RFC is 433.1.204 which covers the case of the OCPD being above the cable rating, but due to the ring structure with fused sockets along it, that is acceptable.
It does actually specifically say "protected by a 30A or 32A protective device" in the reg, and says "Such circuits are deemed to meet the requirements of 433.1.1 if the CCC of the cable is not less than 20A". Given that method 103 problems with RFC's are commonly spoken of I'd always assumed that the 20A was "as installed" not "in free air".
So is 2.5 sq mm T+E installed to method 103 hooked up to a 20A OCPD arranged as an RFC allowed?
And is any installation method with a 20A OCPD arranged as an RFC allowed?
Discuss! And let's keep this civil - it's Christmas!