I

iwire4

I have recently changed the consumer unit on a clients house. I even carried out insulation resistance testing on the existing circuit prior to installation to prevent any problems later. All was well until the light in the stairwell was switched on and it tripped both RCD's! two circuits (upstairs and downstairs lighting on separate RCD's) I looked at the wiring for the light and could see it had been modified through a junction box. It had the live feed from the downstairs lighting circuit and the neutral was from the upstairs circuit. It would appear this was done when the new extension was built to enable the lights to be switched on and off at three locations. I scratched my head and tried to work out a 3way switching solution with the existing wires. I was stumped. I have returned it to the existing two way switching. This means that there is no tripping but it has left my customer unable to switch the hall light off from the new extension. I have tried to work it out in the meantime to no avail, hence this post.
I'm sure this is regular occurrence when a house is extended?
The downstairs switch has 3 core and earth to the switch in the upstairs hallway. Twin and earth runs from this switch to the light rose (conventional 2way wiring). The additional switch in the new extension has 3 core and earth to the attic (not connected at present). I have to use what is existing as I can't replace the wires without major re-decorating required.
Has anyone come across this on their travels? Can it be done with what is in place?
RCD's are great but bring with them their own little problems.
Ian
 
the dreaded borrowed neutral. easiest way to fix is to put both lighting circuits on the same RCD if a proper fix entails major redecorating.
 
Agreed with above, but also you would have to put all lighting on same MCB , as you cannot share neutrals on seperate MCBS either , poss upgrade to 10A MCB
 
You will need an intermediate switch. also you will need to be able to access the exiting 3 core with the view to connecting the new three core to it, or the new three core will have to go to one of the switches. If you can fulfill these requirements then it's just a matter of juggling the wires at the switch
 
Thanks everyone. No magical cure out there then. I don't feel so bad now. Will take on board your comments and give the good news to my customer. Cheers.
 
Tels right, end of, put both feeds on the same rcd, infact you could break regs by putting them on the same mcb also haha, but don't tell anyone I mentioned it.
 
There is another guy who would do it all live, ..........Martom ..................
not sure if he would be alive after though
 

Reply to 2way to 3way switching in extension in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
884
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
581
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
344
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock