Discuss 3 Phase motor windings Resistance Calculations ? in the Canada area at ElectriciansForums.net

T

TailSpin

Hi All

Is there a calculation for working out an unknown resistance on a 3 Phase Motor ?

The rating plate has 15kW / 29 amps . Trying to remember from my collage days but it has been a while.

Regards

Tailspin

:confused:
 
just curious,but why do you want to know? i would say the winding resistance of a 15kw motor would be close to zero while on small motors you would get much higher, if checking look for 3 very similar readings. cant think of a calculation other than R=P/I^2 but dont think that would work for 3 phase where P=SQ RT3*V*A*PF, so in summary, sorry!, i dont know:confused::)
 
me neither. would just expect a fairly low ohms reading on each winding, but would expect them to be almost identical. load is mainly inductive.
 
The motor in question is one that a work collage had to investigate. It had winding readings as follow : 4.02 / 2.62 / 3.18 ohms . I know the resistance readings should be closer together. He did manage to record some current readings of : 5.1 / 5.6 / 6.1 Amps. The motor was running freely with no other apparent problems. So I was convinced it was a winding issue . Insulation resistance check carried out with no problem. Which is why I thought it would be nice if the resistance could be roughly calculated.

Regards

Tailspin ;)
 
just checked the electrodroid app on my phone which contains a resistivity and temp coefficent table. the resistivity of copper at 20 degrees C is 1.67*10^-8 ohms per meter, so now all you have to do is unwind the winding and get a tape measure on it;)
i agree your ohm readings are a bit off but your running current check seems ok,
what make are the instruments and when where the batteries last changed?
sorry couldnt be of more help.
 
Is the motor 6 wires ? Connected in star or delta ?

Could be a loose connection, disconnect the links check all terminals, measure the resistance of each individual winding (preferred cold) and they should be near enough the same on a cheapo meter. There may be a small difference depending on how the windings are laid down. For a 15Kw you will be down in the less than 5 Ohms range.

With a lift the windings will be the same resistance near enough. 3 Layer wound then the windings will have a small difference between the three.
 
The motor I believe is wired in star , and the meter used was the Fluke Insulation resistance tester which has a low resistance range.

Thanks All for your thoughts , motor now sent to be sorted by motor specialist .

I did like the idea of running out the windings and measuring them


Regards
Tailspin
 

Reply to 3 Phase motor windings Resistance Calculations ? in the Canada area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
647
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
749
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock