Discuss 3 Phase power keeps on tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Hi Guys any advice on this one will be a major help.
Was called out to a loss of power turned up expecting a breaker down as usual but not the case.
so here goes the problem- an apartment block with 315 amp incoming fuses feeding 400 amp mccb set to trip at 220. This in turn feeds a rising busbar with several tap off units and 250amp mccb feeding the apartment fuses and meters. No faults show when tested out but every night it trips taking out the 400amp mccb and all three main fuses.
Anyone any ideas on why this is happening. Please help as at my wits end with this one
 
Taking out all of the three main fuses suggests overcurrent as opposed to a fault. Sounds like you need to put some monitoring in place as well as asking if someone has recently installed an item of three phase equipment which is tipping the balance. EV chargers?
 
Taking out all of the three main fuses suggests overcurrent as opposed to a fault. Sounds like you need to put some monitoring in place as well as asking if someone has recently installed an item of three phase equipment which is tipping the balance. EV chargers?
Sorry meant to to add that I was originally thinking overload. Fitted some monitoring and max load was around 200amps. But it did register a huge spike of 1900amps but only for a duration of 2 cycles
 
Last edited by a moderator:
A crude check using Schneider's on-line tool confirms that a 220A MCCB has limited selectivity with a 315A fuse but it ought to be able to protect against typical overload scenarios depending on model/settings. Below shows that model and guessed settings could be selective to the 2kA surge you report
220A-MCCB-315A-fuse.png

However a 2kA surge should take at least 1s to blow those fuse, i.e. about 25 times the period your monitoring shows!
 
Hi Guys any advice on this one will be a major help.
Was called out to a loss of power turned up expecting a breaker down as usual but not the case.
so here goes the problem- an apartment block with 315 amp incoming fuses feeding 400 amp mccb set to trip at 220. This in turn feeds a rising busbar with several tap off units and 250amp mccb feeding the apartment fuses and meters. No faults show when tested out but every night it trips taking out the 400amp mccb and all three main fuses.
Anyone any ideas on why this is happening. Please help as at my wits end with this one
Is the supply to each apartment single or three phase and how many apartments are there
Sorry meant to to add that I was originally thinking overload. Fitted some monitoring and max load was around 200amps. But it did register a huge spike of 1900amps but only for a duration of 2 cycles
So does this happen at roughly the same time everyday and what voltage do you have when it occurs
 
Hi Guys thanks for the responses
To update and answer the other questions.
Yes all apartments are single phase total of 66 split over the phases.
The three main fuses blew at the same time as the monitored spike. It has been tripping and blowing the fuses at a similar time ever day this week but strangely didnt trip last night Saturday
 
New apartment block or a few years old? Just started happening? What space and water heating - off peak time switched electric? EV chargers of 7kW or upwards and are they time controlled to use off peak leccy? Fresh water pumps topping up roof top tanks overnight? Phase currents and voltages balanced? Are phase to N PSSC similar? Are time switched loads all turned on at the same time perhaps and all drawing current until each load starts to randomly cycle on/off ie no staggering or sequencing to promote diversity?
 
Last edited:
New apartment block or a few years old? Just started happening? What space and water heating - off peak time switched electric? EV chargers of 7kW or upwards and are they time controlled to use off peak leccy? Fresh water pumps topping up roof top tanks overnight? Phase currents and voltages balanced? Are phase to N PSSC similar? Are time switched loads all turned on at the same time perhaps?
Apartment block about 8 or 9 years old. Had a couple of issues in the past. The feed in question only serves the apartments water pumps lifts etc on a different incomer
 
Hi Guys thanks for the responses
To update and answer the other questions.
Yes all apartments are single phase total of 66 split over the phases.
The three main fuses blew at the same time as the monitored spike. It has been tripping and blowing the fuses at a similar time ever day this week but strangely didnt trip last night Saturday
Any voltage surge/outage then?

I'm wondering if something upstream is causing voltage to cycle off/on and surge killing it?

Still, it suggests the MCCB is not set to be selective with the fuses, and it still is not enough of a surge for 2 cycles to take out those fuses. What is the max current the monitor's CT can actually record?
 
New posts

Reply to 3 Phase power keeps on tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
678
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no...
Replies
35
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock