Discuss Home Lathe with 3 Phase inverter tripping mains in the DIY Electrical Advice area at ElectriciansForums.net

Wicked

DIY
Reaction score
5
Hello - hope someone can advise please.

I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster 410)

Lathe all works fine but regularly trips my RCCB 80A 30mA breaker taking out half of the board - usually when first powering on. The inverter is plugged into my downstairs ring main which has a Crabtree MCB B32 breaker but it is always the RCCB that trips.

A PAT test of the inverter reveals that Ileak is 7.29mA which I understand is over the limit of 5mA and is therefor a fail.

The manual for the inverter says that if a RCD is used it must be an RCD Type B. The downstairs ring is protected by a Crabtree MCB 32A

Lathe works just fine if I power it from my inverter generator (no Ground of course)...

There is an option on the inverter to remove the Y Capacitor link if it is used on an ungrounded supply - but I guess that will have safety issues.

So anyone have any ideas to stop the inverter tripping the mains (I'm guessing the fact that it is also an inductive load doesn't help)

Thanks

Dave
 
It would be better if it could be fed from a dedicated RCD/RCBO rather than sharing with several other circuits. The combined leakage on your existing RCCB could be on the threshold of its trip point.

I'm no expert on inverters but some of the other members are very knowledgeable and might have some good advice.
 
Thanks but I can’t do that unfortunately - no easy way to get a new cable from the board to the location of the lathe.

Would changing the MCBO for a switch and changing all the MCBs for RCDs be an option on this half of the board?
 
I have a customer with lots of small machines that are regularly moved around to suit the work they are doing at the time.
most of the machines that have inverters in them were troublesome when plugged into rcd sockets.
we have slowly worked round the ones that trip rcd’s and installed an isolating transformer in each one.
problems have now gone away.
 
I have a customer with lots of small machines that are regularly moved around to suit the work they are doing at the time.
most of the machines that have inverters in them were troublesome when plugged into rcd sockets.
we have slowly worked round the ones that trip rcd’s and installed an isolating transformer in each one.
problems have now gone away.
Thanks - is there such a thing as an isolating transformer that can be plugged in to the ring main then the 13A plug on the inverter plugged in to the transformer?
 
Not as far as I know.
it could be added to the machine control panel though.
 
There are isolating transformers available in plastic or metal cases that offer a built in 13A mains socket to feed your equipment.
 
https://www.NoLinkingToThis/p/carro...Vg853Ch2ahg8fEAQYASABEgK98fD_BwE&gclsrc=aw.ds
 
https://www.NoLinkingToThis/p/carro...Vg853Ch2ahg8fEAQYASABEgK98fD_BwE&gclsrc=aw.ds

Exactly what I was thinking of. Many TV repair people used these. That's television, not transvestite. But that's nothing against any transvestite television repair people. Mmm, think I covered that ok.
 
Thanks both - at the risk of being accused of being premature (hate it when that happens :) I found that exact device in the Screwfix catalogue and ordered one earlier on today - I'm picking it up tomorrow. Assuming I don't burn the house down or electrocute myself I'll report back tomorrow.

Looking at the instructions on the Inverter it says I must cut the Y Capacitor link if using it on an ungrounded supply. When I run the inverter powered by my Pure Sine Wave petrol generator it works just fine, and I guess that is seen as an ungrounded supply. I'll try it with the new isolating transformer and se what happens first before cutting the link.

Thanks all for your helpful advice. Dave
 
Just an update - the Isolation Transformer from Screwfix fixed the tripping problem - so thanks to @James and @DPG for the advice.

You have also probably saved my marriage as the risk of tripping the mains during an episode of Classic Coronation Street was just too great!

Thanks

Dave
 
Just an update - the Isolation Transformer from Screwfix fixed the tripping problem - so thanks to @James and @DPG for the advice.

You have also probably saved my marriage as the risk of tripping the mains during an episode of Classic Coronation Street was just too great!

Thanks

Dave

Excellent. To be fair it was James who solved this one.

Got to say I would sooner be in the garage watching the lathe than in the house watching Coronation Street 😀
 

Reply to Home Lathe with 3 Phase inverter tripping mains in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Hi All Let me start by saying I have my 2365 level 3 but never worked in the industry so my knowledge is limited. My partner and I recently...
Replies
22
Views
2K
I’ve a fuseboard as pictured, which has been nuisance tripping on the downstairs ring final circuit. It started off with 32a breaker tripping...
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock