Hi lads 5 year safety inspection the spark put the tails back and later line 2 of the 3 phase blew blowing the box off the wall and taking out the main fuse on the same line into the building can you all just say quickly what you think the spark may have done wrong ?
Cheers
IMG-20230317-WA0026.jpg
 
Last edited by a moderator:
Hi lads 5 year safety inspection the spark put the tails back and later line 2 of the 3 phase blew blowing the box off the wall and taking out the main fuse on the same line into the building can you all just say quickly what you think the spark may have done wrong ?
Cheers
Why did the spark have the tails out for an inspection?
 
Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.

If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.

As Westwood, it looks like a dead short, especially with the ball of copper
 
Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.

If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.

As Westwood, it looks like a dead short, especially with the ball of copper
Yep now bear in mind all other tails and switches are pristine is there any votes for system overload the main fuse that blew into the building is also on phase 2
 
Needs to be powered down and clamp removed, i can see it is already pinching the RHS cable sheath.

Once clamp removed photograph the back side of it, remove the LHS cable and photographc the back plain of board, should tell you everything you need to know, Merry Xmas
Hi can't thank you enough for the advice what would photos of the back of the clamp and board show or what should I look for ?
 
An overloaded board but it's run fine for 5 years and it just happend to blow a few hours after they wiggled the wires plus each phase is perfectly balanced with 9 feeds
That wasn't an overload that was a dead short, a short they created.
 

Reply to 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock