Discuss 3rd Floor Flat Lost Main Earth in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Hi All

3rd floor flat has incoming supply via Conduit which was being used as the earth. Conduit at some stage has failed leaving the property with no suitable earth.
Would it be necessary to run a new sub mains and renew the supply also or is it within the regulations to run a separate earthing conductor (although it would take a different route via the outside of the building).
And additionally to this, as it could be the case with more than one flat would it be acceptable to install a Marshalling Earth Terminal to potentially connect to the other 3 flats on the floor should they have the same issue?

Supply to building in TNS

Any advice is appreciated

Thanks
 
I don't see a objection to running a separate EC so long as it is installed correctly in its own right. So the MET in the property can be reliably earthed but what about the conduit? We know that there is at least one break in its continuity; so long as there's only one it can all still be earthed from the two ends. But perhaps it is high-resistance all over the place and parts of it cannot now be effectively earthed, or perhaps it has completely rusted through and the cables are exposed? I would want to get an idea of what state it is in before making a decision that it is safe to leave the submain cables within it in service.
 

Reply to 3rd Floor Flat Lost Main Earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
553
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock