Discuss Adding a mains plug to a FCU in the UK Electrical Forum area at ElectriciansForums.net
Depends on:Hi,
Can anyone give me some advice on how I add a mains plug to the following circuit,
The FCU is connected to a home alarm system and I would like to add a normal plug socket, any advice would be greatly appreciated
Thanks
View attachment 39684
View attachment 39685
View attachment 39686
What size his the cable 1.0mm2 1.5mm2 or 2.5mm2?
You can if you go through a fused spur! Appendix 15 BS 76571Firstly i would get that supply to the alarm sorted out it looks
Like the supply cable, is run with the alarm cables and very close to pipe work, also as morduch says if thats on a 32 amp fuse you can not spur of it with a socket as you only can have one point spured off the ring circuit , that if is a ring ,
Firstly i would get that supply to the alarm sorted out it looks
Like the supply cable, is run with the alarm cables and very close to pipe work, also as morduch says if thats on a 32 amp fuse you can not spur of it with a socket as you only can have one point spured off the ring circuit , that if is a ring ,
Reply to Adding a mains plug to a FCU in the UK Electrical Forum area at ElectriciansForums.net
We use essential cookies to make this site work, and optional cookies to enhance your experience.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.