Discuss Adding extra chime to mains wired doorbell in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi
I have a mains wired doorbell with the chime in the hallway. Parents are elderly and dont hear the bell all the time. I want to run two wires from the hallway chime into living room and add another chime there. Does the new chime need to have built in transformer does it not require it?
Current set up is a transformer by the fusebox and the chime has one wire to it and another to the push button. One wire from the push button the transformer to complete circuit.
 
One transformer for two chimes

But

I have found that many bell transformers don’t have enough output for two bells. So, you may find that you need to replace the tranny. Try it and see if it works, but I too would go for a wireless jobby.
 
Connecting two chimes with built in transformers to the same push is not a good idea. They would need to be connected so that booth transformers are phased together, and not one 180 degrees out from the other, and unless the voltages of the transformer secondaries are identical, there will be a constantly circulating current through the two chimes, which may make them buzz. you could probably solve this with a couple of blocking diodes, but then the chimes might not perform as intended.
You can connect two chimes in parallel with a transformer by the CU, as long as that transformer can supply sufficient power to supply your chosen two chimes.
 
You can connect two chimes in parallel with a transformer by the CU, as long as that transformer can supply sufficient power to supply your chosen two chimes.

Thanks. So just buy a normal chime like i got already without a transformer built in. Wire it from the current chime. As long as transformer i got currently has sufficient power. Ill check it tonight and advise what power it has.
 
Yes, but as I suggested in an earlier post, I suspect that there are electronic chimes available that use a lot less power than a conventional one with a solenoid slug hitting a tuned piece of metal.
 
You can connect two chimes in parallel with a transformer by the CU, as long as that transformer can supply sufficient power to supply your chosen two chimes.

Thanks. So just buy a normal chime like i got already without a transformer built in. Wire it from the current chime. As long as transformer i got currently has sufficient power. Ill check it tonight and advise what power it has.
Most standard bell transformers are rated at around 1amp. Enough for one bell. Adding a second bell may be too much.
And the length of the wiring has an effect too. But see how you get on. Be prepared to have to buy a bigger transformer.

Quite honestly you’d be better off ditching the plan to extend the existing bell. Get a wireless one with two (or more) soundest. It will probably be cheaper and easier.
 
Any recommendations?
Range topper
Middle of the road
Budget
I can only recommend one I have experience with and use.
The Lloytron doorbells use their MIPS system, so you can buy the basic push button + sounder and then add more sounders and bell pushes.

Mine works well. Has a good range. Note that wireless operation can be affected by some building structures, but they work well in standard type houses.

Lloytron B7505BK 32-Melody Mains Plug-In Wireless Door Chime with MiPs - Black Lloytron B7505BK 32-Melody Mains Plug-In Wireless Door Chime with MiPs - Black : Amazon.co.uk: DIY & Tools - https://amzn.eu/d/fjfPM6c
 

Reply to Adding extra chime to mains wired doorbell in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, A lot about this fault confused me to be honest. So customer complained the doorbell was not working as intended. By that I mean the chime...
Replies
2
Views
695
Hello, I would liked to install a Byron wired doorbell with built in chime and 8v transformer. I'm struggling to get power source. I have a...
Replies
1
Views
437
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi, So I ended up with a Ring video wired doorbell instead of a Byron video wired doorbell as B&Q were out of stock (had ordered online) and they...
Replies
1
Views
952
Help please! Got this to use as a doorbell but unsure of specifics and wiring. If someone could maybe help with a diagram/specific parts or even...
Replies
11
Views
473

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock