A
amckay
Is there anything wrong with this scenario.
Customer wants two extra socket about 2m from each other, first one being 400mm from consumer unit.
No spare ways on CU, nearest outlet on rfc is 5m away.
Is it possible to just add a radial fed from the MCB which feeds the rfc for that floor?
I'm thinking its just bad practice to do so but can find info in osg.
MCB rated at 32A and protected by 30mA RCD.