Additional consumer unit in domestic property breaker sizes?

Discuss Additional consumer unit in domestic property breaker sizes? in the UK Electrical Forum area at ElectriciansForums.net

P

P-Courty

I have a few questions about a couple of breaker sizes needed due to current draw and diversity.

In place already is as usual;
A main service fuse (100A)
25mm P&N tails to meter
25mm P&N tails from meter to CU
12 way CU split load

What has been done is a garage conversion to kitchen.
I was told they wanted a new CU for the kitchen area due to the 12 way being full and old (and strapped for cash).

I've been given a 6 way CU with 80A RCD, P&N 25mm tails & 16mm earth tail (customer supplied).

My plan was (correct me if I am wrong anywhere please) going to need additional items to complete.

1. Outgoing 25mm tails from meter to a 2 way CU with an MK 100A double pole main breaker (to protect service fuse).
2. From there 25mm tails to a 6 terminal henley block.
3. From the henley block 25mm tails to new 6 way CU and 25mm tails to existing CU.
4. 16mm earth to each CU from MEB.

Now this is were I could do with a little help on breakers.

The new board only has the RCD, do I need a main breaker in there? As in an 80A main and 63A 30mA RCD?
The circuits put it are a 32A kitchen ring final and a cooker circuit (for some reason in a 2.5mm t&e) I did question that and they said the kitchen fitters said the 2 single ovens are capable of being on 16A radials and the hob (not heard that before) so I may need to upgrade the cable size for that when I find out the kw of them (think it will be a must). This is what is confusing me on the RCD and main breaker sizes I should choose as i'm not completely sure what the draw is going to be.

Any help on all of this would be very much appreciated as they want this completed by the end of this week.

Thank you in advance for any help and advice given.
 
MK do not make 100A double pole circuit breakers.

In this country we don't fit main breakers in CU's

I shouldn't worry about the kitchen wiring too much, whoever has installed it will be connecting it and signing it off.
You obviously won't be doing this as only the person who installed it can do the sign off or LABC.
 
Hold on. Who's designing this? You or kev the kitchen fitter?

The circuits are already in and the client done what the kitchen fitter told him and put 2.5mm in (looks like i'll be changing that).

I did ask for the ratings off the client but all he would tell me is " the kitchen fitter said they can go on 16A 2.5mm radials" (he's one of those people who say your wrong because someone older than you has told them different)

So all I have now been asked to do is put this board on so for obvious reasons I want to make sure that the RCD and main breakers are correct and adequate for the protect of the circuits.
 
The circuits are already in and the client done what the kitchen fitter told him and put 2.5mm in (looks like i'll be changing that).

I did ask for the ratings off the client but all he would tell me is " the kitchen fitter said they can go on 16A 2.5mm radials" (he's one of those people who say your wrong because someone older than you has told them different)

So all I have now been asked to do is put this board on so for obvious reasons I want to make sure that the RCD and main breakers are correct and adequate for the protect of the circuits.

If you did not install the circuits then you do not connect and test them, it's pretty simple.

In domestics the design, installation and IV is done by the same person who then signs it off. There is no scope for anyone else to sign off other than LABC


I'll say it again, we don't fit main breakers in CUs nor would it be necessary or appropriate.
You also need to ensure bonding and everything else is up to scratch before starting on any such works
 
Mate, if you're not an electrician then you need to get one.
If you are then you need to start acting like one.

Now that's a bit aggressive isn't it I am only trying to ask what I thought was a friendly community of electricians for advice I'm sure back when you started as an electrician you used to ask questions and hope people would be helpful to you too sorry if I've some how touched Ă  nerve but I am only asking for help and guidance
 
So you would take the 25mm tails straight from the meter to a henley block then to the individual boards with no other isolation than only the main service fuse?

No I wouldn't, the service fuse is not there as a point of isolation for the installation. Hence why it is sealed and we are not allowed to remove it!

I would install a main switch as required by the regulations and wouldn't use a Henley block if I could help it.
But then I wouldn't be doing a job which involved connecting up a DIYers bodgery
 
I have checked all equipotential bonding is in place and back to the MEB the circuits aren't going to be connected by me i'm just putting the board on from the main supply that is all i have been asked to do.
 
Now that's a bit aggressive isn't it I am only trying to ask what I thought was a friendly community of electricians for advice I'm sure back when you started as an electrician you used to ask questions and hope people would be helpful to you too sorry if I've some how touched Ă  nerve but I am only asking for help and guidance

Are you an electrician?

Trev and I and most people here qualified through an apprenticeship where we were taught all of this.
 
No I wouldn't, the service fuse is not there as a point of isolation for the installation. Hence why it is sealed and we are not allowed to remove it!

I would install a main switch as required by the regulations and wouldn't use a Henley block if I could help it.
But then I wouldn't be doing a job which involved connecting up a DIYers bodgery

So you would put a main switch between the meter and henley block? Thats what i was on about ...
 
Mate, when I started out I was closely supervised by a properly qualified man who only ever let me do things when he was convinced I had the ability to do them.
I'm happy to help people but your questions show a lack of training to me. If I'm wrong then I'll apologise and help as much as I can.
It isn't my intention to be aggressive but I'll clarify what I said , if you are going to be the electrician on this job then YOU have to take charge of it. YOU are the one (allegedly) with the training and expertise to do it correctly, not Kev the kitchen fitter. If necessary you tell him to go forth and multiply and stick to what he knows because you have a greater degree of expertise in electrical matters than him.
That's what I'd do anyway
 
Are you an electrician?

Trev and I and most people here qualified through an apprenticeship where we were taught all of this.

And I too went through an apprenticeship and done my 17th edition 3 years ago and unfortunatly fell into a situation of not being able to get work so have been a labourer for 3 years and need to get back up to scratch on what i was qualified to do which is why i thought i would ask friendly electricins with more experience for a bit of help and guidance to get me back in the right position to get myself up to scratch
 
And I too went through an apprenticeship and done my 17th edition 3 years ago and unfortunatly fell into a situation of not being able to get work so have been a labourer for 3 years and need to get back up to scratch on what i was qualified to do which is why i thought i would ask friendly electricins with more experience for a bit of help and guidance to get me back in the right position to get myself up to scratch

Why did you do the 17th course if you served your time under the 17th? Your NVQ must have been under 17th regulations?
 
It was but I had to pay to do a 17th edition regulation course separate to the 3 years of college and the nvq level 3 portfolio. When I was going through my apprenticeship the regs went through the change from 16th to 17th as when i started college we used 16th ed. Books
 
It's a con!

And it appears that despite doing the 17th qualification people don't even know the difference between a breaker and a switch and when to use them

How am I conning you, I am asking for help off you if I was regular Joe Blogs I would just go ahead and do it. I got all my certificates back in January 2012 I've been labouring since then (2 years 11 months) basically 3 years like I said. In that time I had a lot of family issues I went through lost everything and hit depression and am now in financial difficulty so sorry if this the words breaker and switch got mixed up in my head during all of this.

I've come here to ask you guys for help because surely you've needed that in the past. And if this is childs play then why are you not helping me and just tearing me back down to were I used to be I thought coming to you guys could help me out.

It looks like you have never been living on every penny you get and own your own houses and have vans well to me a penny is a lot and as for a car well thats a luxury to me and my bloody pedal bike. I thought you guys could help me out but guess I was wrong. I have my A's back from school and distictions from college I worked my arse off to be told I was over qualified for certain jobs so can't even work on a till at my local Asda because of that so sorry for asking for help!
 
Okay sorry about the rant just been through some bad things, anyway the client in question was my uncle and was just trying to help him out a little but I'll do what you lot said and tell him to phone a local electrician with more knowledge than me to do it as I guess I'm just to rusty for this now. Apologies if I offended any of you in anyway.
 

Reply to Additional consumer unit in domestic property breaker sizes? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock