An insulation resistance test

Discuss An insulation resistance test in the UK Electrical Forum area at ElectriciansForums.net

akmal

-
Reaction score
0
Hi,

Can some one please help me with this question:

Q: An insulation resistance test on one of the radial socket-outlet indicated zero mega ohm between line and neutral. Explain why the result of the previous R1 + R2 test could not be used to confirm polarity for this circuit.

If any one can answer this question, it will be very appreciated.

Thanks
 
Is this a homework question? We will gladly help you, but firstvshow what you think is the answer, then we will help and point you in the right direction.

If you are a trainee there is a section on here just for trainees, which you may want to join.
 
Hi,

Can some one please help me with this question:

Q: An insulation resistance test on one of the radial socket-outlet indicated zero mega ohm between line and neutral. Explain why the result of the previous R1 + R2 test could not be used to confirm polarity for this circuit.

If any one can answer this question, it will be very appreciated.

Thanks
it might be worth signing upto the trainee section.

we dont do peoples homework for them.

what do you think?

what is an ir test? what is the difference between 0.00 and 999M ohms on ir test?

what would it mean if you got 0.00 on the test


R1 = L
R2 = cpc
Rn= N
 
Hi,

Can some one please help me with this question:

Q: An insulation resistance test on one of the radial socket-outlet indicated zero mega ohm between line and neutral. Explain why the result of the previous R1 + R2 test could not be used to confirm polarity for this circuit.

If any one can answer this question, it will be very appreciated.

Thanks

Come on now put your thinking cap on, R1=res of line conductor
R2= res of cpc
RN =res of neutral
got it so far? and you have a line to neutral short 0Mohms, yes? so what do you the R1+R2 test will actually measure? rocket science it is not. Hope thats the right way to describe it, I have just got in from doing the shopping, I'm stressed.
 
Hi dude, So you have a "link" ,of unknown impedance,between R1 and Rn...and a continuity reading (presumably in Ohms) between R1 and R2.

If you draw it out,it may become clearer. :icon12:
 
If the question really uses the phrase "mega ohm" I'll show my arse in a shop window

Got a feeling Trev it should be Megohms all one word, not as some call it megger ohms mega ohms. but love to see your bare arse in a Tescos extra lol:laugh::speechless::speechless:
 

Reply to An insulation resistance test in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock