Hi everyone. Hello from Poland
My uncle give me inverter Aurora Pvi 3.6
He told me when disconnect Pv panels the cable made a short circuit to the ground
I open it. Inside its nothing burned (I think)?
When I connect to AC grid inverter not start. No errors, no message BTW it's dead ?
Maybe someone have this same problem?
I hope that you will be able to help me even though I am from Poland and my English is not the best
 
I don't know the answer to your problem, but you're English is pretty good.
 
1) Check isolators, circuit breakers, etc are in the correct position.
2) Undo the front cover and check the AC connection - are the live/neutral/earth wires in the correct terminals?
3) Test the AC voltage at the inverter.
4) Test the strings. Have you got voltage? Is the voltage within the inverter's operating range?

If you have DC voltage but no AC, the screen says: "Missing Grid".
 
1) Check isolators, circuit breakers, etc are in the correct position. - he has a fuse or whatever?
2) Undo the front cover and check the AC connection - are the live/neutral/earth wires in the correct terminals? - it's OK
3) Test the AC voltage at the inverter. - AC from grid it's OK
4) Test the strings. Have you got voltage? Is the voltage within the inverter's operating range? - it's OK

If you have DC voltage but no AC, the screen says: "Missing Grid". - the display does not turn on
 
Take the inverter to a friend's house and try it there ? Bring their inverter to your house and see if it works ?

You could also try contacting a local solar installer to come out and look at it for you.
 

Reply to Aurora power one 3.6 not start in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top