Search the forum,

Discuss Bit confused here, IR testing. in the UK Electrical Forum area at ElectriciansForums.net

Thommo

Trainee
Reaction score
60
Hi all, this is probably a daft question to most of you.
At training centre I have started dead testing. When I get to the 3 point IR test on a single circuit should I switch off the breaker for that circuit .Hopefully I am correct in removing any lamps on a lighting circuit and turned switches on with all points closed. On a radial or final ring I have closed all points turned sockets on.
I think the procedure may be different when doing a global test, not sure.
Just a bit confused about the circuit breaker as I know it is switched on for continuity of cpc test.
Thanks in advance for any input
 
Hi all, this is probably a daft question to most of you.
At training centre I have started dead testing. When I get to the 3 point IR test on a single circuit should I switch off the breaker for that circuit .Hopefully I am correct in removing any lamps on a lighting circuit and turned switches on with all points closed. On a radial or final ring I have closed all points turned sockets on.
I think the procedure may be different when doing a global test, not sure.
Just a bit confused about the circuit breaker as I know it is switched on for continuity of cpc test.
Thanks in advance for any input
dead testing is what it says. all dead tests (continuity,polarity, and IR) are carried oit with the circuit/s isolated from supply. on new installations, these tests are done even before the circuits are connected or the CU powered up. don't confuse continuity with loop impedance. the latter is a "live" test.
 
dead testing is what it says. all dead tests (continuity,polarity, and IR) are carried oit with the circuit/s isolated from supply. on new installations, these tests are done even before the circuits are connected or the CU powered up. don't confuse continuity with loop impedance. the latter is a "live" test.
Thanks telectrix,
Here’s why I am a bit confused.
Here’s a page from my notes I have been given. I have underlined the reason I am confused.
 

Attachments

  • 9A29A114-D94D-4D7C-A0AF-D78C29643D23.jpeg
    177.9 KB · Views: 38
You can test circuits for IR individually, or globally. Globally with the breakers on, in order to link them together......more than one circuit, one test, as in many EICR's. Whichever, supply to the breakers must be isolated. It's a dead test.
 
You can test circuits for IR individually, or globally. Globally with the breakers on, linking them together......all one test, as in many EICR's. Whichever, supply to the breakers must be isolated. It's a dead test.
So the answer contradicts my notes. And confirms the way I have been doing it this week, with circuit breaker in the off position
 
No, either way. With IR you're checking for clearance. If everything is 'clear' from each other with a global test, it's OK. If not, you have to split the circuits and test individually to find which is faulty.
With continuity, you can link the breakers, switched on, to earth. Then test at the end of circuit for continuity. If RFC's are involved, each circuit has to be done individually.
Whichever ways, the power is OFF.
 
No, either way. With IR you're checking for clearance. If everything is 'clear' from each other with a global test, it's OK. If not, you have to split the circuits and test individually to find which is faulty.
With continuity, you can link the breakers, switched on, to earth. Then test at the end of circuit for continuity. If RFC's are involved, each circuit has to be done individually.
Whichever ways, the power is OFF.
Thanks ipf clarity . So I haven’t been doing it wrong then.
 
Thanks telectrix,
Here’s why I am a bit confused.
Here’s a page from my notes I have been given. I have underlined the reason I am confused.
You might want to challenge your tutor on that as it potentially dangerous to carry out IR testing on live circuits.
 

Reply to Bit confused here, IR testing. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
669
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
705
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock