Search the forum,

Discuss Bit of a mystery to me, any ideas? Fault on three phase Merlin Gerin in the UK Electrical Forum area at ElectriciansForums.net

Vortigern

Esteemed
Arms
Reaction score
2,389
Outage of main three phase primary switch box for one of three buildings on commercial site. The building houses around 30 commercial units. Switched back on the main switch, power restored. Except for one unit. All units supplied through the secondary sub switch box. Large MCCB MEM type.

Three phase and single phase off to units. The unit that did not switch back on was a three phase unit, sub main, Merlin Gerin TP+N. All single MCBs to ring circuits and lighting. Nothing unusual power wise just an office been there since 1992. Took off cover of DB and found the central spine the MCBs attach to showed signs of a short or major blow out.

I enclose pictures of the interior of that spine/bus bars with the top removed to examine the short. Only problem is there was not a short. You can see the carbonisation. The MCBs were not damaged at all. There were no foreign objects or loose parts yet there must have been an arc over or something. People in office said they heard a bang. They were doing nothing out of the ordinary. There were no vaporised metal parts.

The upstream supply at the MEM MCCB had popped off. I put it on and put the spine/bus bar together and switched on Merlin DB without load. Progressively switched on each circuit, waited an hour or so, nothing, everything worked fine. Zs at all sockets as the epi center of the carbonisation was on the 32a MCB. Zs was fine for all circuits. 3 rings radial/3 lights/other 7 in all.

Any thoughts? a million to one chance of a massive surge at that box across phases???? Never seen this before and I have dealt with a lot of Merlin Gerin. Sorry about the picture quality but at least it gives an idea of what I am talking about. Gonna change the box but just curious as to the why.
 

Attachments

  • IMG_1274.JPG
    106.3 KB · Views: 79
  • IMG_1276.JPG
    88.1 KB · Views: 66
  • IMG_1285.JPG
    103 KB · Views: 68
  • IMG_1276.JPG
    88.1 KB · Views: 72
Last edited:
The third picture is of the sliders you get with Merlin Gerin bus bars to disconnect the power from the live tang. Could be an arc from one of these, but still, why.
 
Pretty certain there was something in there that shouldn't have been there. Whether debris from installation that happened to move, or something that walked in there by itself. Probably something non-metallic if there's no localised splash anywhere on the bars. Unlikely to be surge-related on a submain, if nothing else in the installation is even slightly damaged.
 
I took it apart on a table that was clear and examined carefully each component. There was nothing floating around or stuck on any component of it. No vapourisation of any of the metal parts at all. All compartments were intact i.e. the plastic separating the the bus bars for each phase. I guess the distance between the phase bars must be at least 10mm. However I take some comfort that you @Lucien Nunes do not immediately see what the problem might be.
 
I think I would be passing it to Schneider for comment, there is clearly an issue to cause the failure and the question that has to be asked is this an isolated incident or are there other boards in service that could suffer a similar failure
 
I thought, well that post sunk like a stone. However a couple of you have rallied and come up with some pointers, always appreciated. Also good to bounce it off others to make sure I am not missing something blindingly obvious.
 
Here is a picture of the three phase bus bar chamber before taking apart that shows the carbonisation. My expectation was to find melted metal parts, but none were found. I might buy the idea that a foreign object such as fauna was abroad in the chamber and got vapourised.
 

Attachments

  • MerlinGblow.jpg
    94.7 KB · Views: 31
Spider?? Not as daft as it sounds
 

Reply to Bit of a mystery to me, any ideas? Fault on three phase Merlin Gerin in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
889
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
892
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
958
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hi all, new to this thread and just looking for some views. I have today attended a industrial unit which is being converted into small...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top