I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing machines.

All the washing machines including those that are single phase have triple pole MCBs installed and wired in 5-core to 16A rotary isolator. from the same isolator a 5-core rubber flex is used and then of those five cores two of the phase L2 and L3 have been WAGO'd in the next single phase washing machine, exactly the same but L1 and L3 have been WAGO'd

Googling this type of things has yielded a mix bag of opinion from stating remove the TP breaker and install a single pole breaker, some have said this is fine as some machine would utilise only a single phase on low-load in any case. Other have said it is okay as the TP breaker would still trip on overload of the single phase being used or on short circuit and have gone as far as saying it's possibly been done where a pre-existing machine used the three phases and now only utilise one.

Would you recommend making safe the other two phases at each end of the cable and installing a single pole MCB? or Would you say that there aren't any issues for this setup?

Any insights or opinions on this one would be grateful.
 
Agree with Dave disconnect unused
Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room in the DB to add other circuits and it also sounds like the loads of been spread out over the 3 phases so all good there.
 

Reply to Three phase circuit breaker - Utilising only one phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
996
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
928
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
742

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock