Currently reading:
board change and cable length?

Discuss board change and cable length? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

phabpixs

Got to do a board change 7 ways currently, but existing cables have been left short as earths on new unit on right hand side instead of left! what is the best/ legitimate way of extending them? main earth & bonding will also need extending!
 
Got to do a board change 7 ways currently, but existing cables have been left short as earths on new unit on right hand side instead of left! what is the best/ legitimate way of extending them? main earth & bonding will also need extending!
Cirmp join them will be fine, a bit of heatshrink would'nt go a miss either but you can't extend the main earth and bonding they have to be a continuous length so they need renewing
 
I would have thought solder etc for main bonding would be ok if nightmare to renew, or use external MET at whatever point old bonding reaches.
 
You would probably find that an interuption would increase the resistance over 0.05 although the earth terminal block idea would be ok, i was just taught to keep them all one continuous length:)
 
you can't extend the main earth and bonding they have to be a continuous length so they need renewing

You need to make your own mind up as only you know the site you are working on. Yes it would be nice to just replace the main bond but in a lot of cases this is just not possible because of decoration etc etc. If you do extend it then it should be a permenant joint such as a through crimp.

Just a footnote.

You can also use one earth bond cable to do both gas and water or other services as long as it is unbroken, you can though cut the cable at the first bonding point if both ends are then put into a lug, therefore if it does get removed then the other services do not get disconnected
 

Reply to board change and cable length? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock