Search the forum,

Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.
Wiring systems are deemed to be double insulated if adequate mechanical protection of the basic insulation is provided by a non-metallic sheath or non-metallic conduit.
 
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.[/QUOTE I would say that any non metallic sheathed cable whether single core, multi or flat t&e affords protection against basic and fault protection contact much like class 2 equipment but isn't to be regarded as class II in itself.
 
To be double insulated you require two layers of "electrical" insulation or a single layer or more of reinforced insulation.
 
Conduit is part of the electrical installation, it doesn't compare with a double insulated (class2) metal light fitting. So would the disbelievers run a 3 core (L,N&E) swa under the floor without earthing the armour?
 
Conduit is part of the electrical installation, it doesn't compare with a double insulated (class2) metal light fitting. So would the disbelievers run a 3 core (L,N&E) swa under the floor without earthing the armour?
The armour needs glanding so by definition is always an exposed conductive part so it’s not the same is it
 
The armour is part of the overall construction of the cable
Conduit is not
Insulated and sheathed cables gives satisfactory protection against basic and fault protection is all I’m saying
 
I would always consider galvanised trunking and conduit containing low voltage cables to be an exposed conductive part. (Likewise the armour of an SWA.) It's not the same scenario as cable tray which is not intended to be used with non-sheathed cables.
 
I would always consider galvanised trunking and conduit to be an exposed conductive part. (Likewise the armour of an SWA.) It's not the same scenario as cable tray which is not intended to be used with non-sheathed cables.
I never said non sheathed cables I said sheathed
 
I know. I pointed out that comparing trunking/conduit with tray is wrong as tray is not intended to be used with non-sheathed cables whereas trunking and conduit are.
I think the op is saying twin and earth cables installed in conduit and not singles.
Singles would always need containment and if metallic then always earthed as it only has one layer of insulation (basic protection) only
 
I think the op is saying twin and earth cables installed in conduit and not singles.
Singles would always need containment and if metallic then always earthed as it only has one layer of insulation (basic protection) only
I am aware of that. I am saying that the fact that trunking and conduit are designed for non-sheathed cables means that they must always be regarded as exposed conductive parts. I am aware that singles aren't being used in the conduit in this instance. (T&E in conduit is generally something to be avoided to be honest, as that isn't what conduit is designed for. I accept that sometimes it is handy to improve the look of drops or provide extra mechanical protection or whatever though.

T&E also only has one layer of insulation though - the insulating properties of the sheath are not the same as the insulation and it is only there to provide mechanical protection.
 
I am aware of that. I am saying that the fact that trunking and conduit are designed for non-sheathed cables means that they must always be regarded as exposed conductive parts. I am aware that singles aren't being used in the conduit in this instance. (T&E in conduit is generally something to be avoided to be honest, as that isn't what conduit is designed for. I accept that sometimes it is handy to improve the look of drops or provide extra mechanical protection or whatever though.

T&E also only has one layer of insulation though - the insulating properties of the sheath are not the same as the insulation and it is only there to provide mechanical protection.
But it would take the basic insulation to fail and the sheath to fail for it to become a hazard not taking impact into account.
Rather than people saying it’s metal it must be earthed my interpretation is not necessarily if using cables such as twin and earth.
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock