Bonding of conduit in kitchen floor

Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
62
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
Because I guess the tray isn’t part of the electrical installation that’s to say it’s not classed as an exposed conductive part it’s only a cable management system.
If you have GN8 I’d have a read of page 164&165.
 
I have earthed basket and tray many times before to follow specification.
so. up aladder checking for a damaged cable. one hand in contact with the esrthed tray. other hand fishing round contacts a live conductor ( insulation damage?). ZAP.
 
Got a belt off a tray with T&Es on it in a ceiling void a few years back. One length run across the void and was isolated from any earth. The cables dropped through the perforations with no protection and one must have been cut through because the tray was live which I discovered when I provided a path for it to the ceiling grid, never say never.
 
I asked a similar question of Elecsa a couple of years ago regarding T&E running through a backbox to identify a drop, before going through a wall. They told me that as long as the T&E is continuous, then the backbox does not need to be earthed, as the cable is insulated and sheathed.
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top