Currently reading:
Burnt neutrals

Discuss Burnt neutrals in the UK Electrical Forum area at ElectriciansForums.net

Theory: people habitually wire the line first, and don't pay as much attention to torquing up the neutral screws.
 
it's all down to electrons. they come all the way from the L supply, race through the installation, heat up your megawatt shower, then they knackered and so are slow on the return trip, spending longer at the N shower terminal for a rest, thereby overheating said N terminall. :smilielol5::smilielol5::smilielol5:
 
hmmm. they used to be OK with black. praps it's colours with a ue in them, anti european, like fagash farage.

Haven't you sorted out that problem with dyslexia ... that's the EU don't you know. << Banter! No disrespect or belittling of those who struggle with real dyslexia meant in any way shape or form. No dyslexics should be offended by this post ... please?
 
here's a burnt live.

20130102_155745.jpg

80A HRC fuse on a 10mm XLPE SWA . i was called out after FB attendance xmas day.
 
Why is it always the neutral that overheats on shower pull switches? I've never seen a burnt live conductor.

I love shower threads so !!

Once current has flowed through a fixed resistance the returning voltage drops.
That drop in voltage creates a back emf that is harmonically amplified by an increase in current.

Now the harmonics become resonant, and over time create mechanical vibration that work the terminal screws loose.
This in turn creates a bad connection producing heat.

So effectively if line and neutral are torqued to equal values, over time it is the neutral that becomes susceptible to a loose connection. :icon12:
 
I love shower threads so !!

Once current has flowed through a fixed resistance the returning voltage drops.
That drop in voltage creates a back emf that is harmonically amplified by an increase in current.

Now the harmonics become resonant, and over time create mechanical vibration that work the terminal screws loose.
This in turn creates a bad connection producing heat.

So effectively if line and neutral are torqued to equal values, over time it is the neutral that becomes susceptible to a loose connection. :icon12:
And you win tonight's star prize for the correct answer.
 
Why is it always the neutral that overheats on shower pull switches? I've never seen a burnt live conductor.

Standard R1+R2 testing on a radial carries out no test on the neutral therefore no poor connection in the neutral will ever be picked up. I'm sceptical about this having any kind of statistically significant part to play though.

You have to bear in mind that on AC, if you ignore potential difference to earth, the neutral spends exactly half of its time being the 'live', really :)
 

Reply to Burnt neutrals in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top