Discuss Calculating 3 phase kva in the Industrial Electricians' Talk area at ElectriciansForums.net

N

nickblake

My brains switched off chaps and i can remember how to calculate 3 phase kva

i know its V x I x 1.73 / 1000

so is it 230 or 400 x I x 1.73 / 1000

fee a right numpty cant belive ive forgotten it not done 3 phase calcs for a while please enlighten me to the correct figures then ill give my self a good slapping:D
 
Example 1

A 415 volt, three phase generator provides 200 Amp. Calculate the kW and kVA of this generator.
kW = V x I P.F. x ÷ 1000 = 415 x 200 x 0.8 x 1.732 ÷ 1000 = 115 kW
kVA = kW ÷ P.F. = 115 ÷ 0.8 = 143 kVA
Example 2

To calculate the current (Amps) available from a 150 kVA generator at 415 Volts
kW = V x I x √3 ÷ 1000 Therefore I = kVA x 1000 ÷ V x √3 = 208 Amps
Example 3

To calculate the size of a generator required to provide 150 Amps @ 440 Volt
kW = V x I x  ÷ 1000 = 440 x 150 x 1.732 ÷ 1000 = 114 kW
 

Reply to Calculating 3 phase kva in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
657
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
wiring a 480 volt 3 phase 114 amp generator to run 2 machines. Both machine nameplate 480 v 3 phase 50 FLA. What size wire and over current...
Replies
0
Views
952
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock