i live in a 1960s built ex-local authority flat. the floors are concrete with approx 30mm of screed poured on top, brick walls. the existing cabling is all MICC which i'm considering ripping out, not because it doesn't work but because i'm looking to move some walls and chase new central heating pipework into the concrete floors. am pretty certain this is going to nick an MICC cable and the circuit will be screwed. not to mention it's not much more expensive to do a full rewire than to find someone who can repair MICC.

QUESTION:if i'm chasing into the screed to run my new cables, is there a risk that i could cut the neighbour's below me lighting cables? is there a chance their lights are running through my screed? (if not, how did they possibly run their lights to their bedroom as their ceiling / my floor is concrete?)

really frustrating job this, if there are any certified NICEIC sparks reading this who are keen to take it on, get in touch. location: dalston, london.
 
C'mon guys, please cut him some slack with the NICEIC thing, he's obviously not in the industry so it wasn't a malicious comment.

With regard to the questions in the OP there's still many sparkies around who can work with the mineral insulated cabling. Secondly with a little time and a cable-finder or tone set there's no reason an experienced electrician couldn't map out the existing cable runs fairly accurately. Finally I'd suggest you have all the circuits tested for continuity and insulation resistance before you plaster up any chases, that way it will be easier to localise any damage you may have caused.
 
C'mon guys, please cut him some slack with the NICEIC thing, he's obviously not in the industry so it wasn't a malicious comment.

With regard to the questions in the OP there's still many sparkies around who can work with the mineral insulated cabling. Secondly with a little time and a cable-finder or tone set there's no reason an experienced electrician couldn't map out the existing cable runs fairly accurately. Finally I'd suggest you have all the circuits tested for continuity and insulation resistance before you plaster up any chases, that way it will be easier to localise any damage you may have caused.

Sorry Marvo. :sad_smile:


Are we still friends?:love:
 
i live in a 1960s built ex-local authority flat. the floors are concrete with approx 30mm of screed poured on top, brick walls. the existing cabling is all MICC which i'm considering ripping out, not because it doesn't work but because i'm looking to move some walls and chase new central heating pipework into the concrete floors. am pretty certain this is going to nick an MICC cable and the circuit will be screwed. not to mention it's not much more expensive to do a full rewire than to find someone who can repair MICC.

QUESTION:if i'm chasing into the screed to run my new cables, is there a risk that i could cut the neighbour's below me lighting cables? is there a chance their lights are running through my screed? (if not, how did they possibly run their lights to their bedroom as their ceiling / my floor is concrete?)

really frustrating job this, if there are any certified NICEIC sparks reading this who are keen to take it on, get in touch. location: dalston, london.

I have not worked in the UK for years but I did work on a lot of high rise buildings when I was there, if the wiring is Pyro (MICC) then it will be clipped to the underside of the ceiling slab of that flat with shallow boxes and plastered over, if it is wired in steel conduit then it will be on the concrete slab of your flat and screeded over, the way to check would be to remove one of your lights and look to see if there are conduits leaving the top of the box and the wiring is PVC insulated or if Pyro enters from the side.
 
I have not worked in the UK for years but I did work on a lot of high rise buildings when I was there, if the wiring is Pyro (MICC) then it will be clipped to the underside of the ceiling slab of that flat with shallow boxes and plastered over, if it is wired in steel conduit then it will be on the concrete slab of your flat and screeded over, the way to check would be to remove one of your lights and look to see if there are conduits leaving the top of the box and the wiring is PVC insulated or if Pyro enters from the side.


If a conduit installation, the conduit runs would be within the slab, installed just after the steel re-bar fixers, with the conduits tied to the re-bar. Never seen a conduit installation run on top of the slab, as for anything else, it would be out of it's installations equipotential zone, if located as you state, especially if were talking for a block of flats situation....
 
Back in my college days pyro was covered with a number of sessions including a number of videos produced by BICC for colleges one of those videos detailed the manufacture and use of what they called the Octopus system this consisted of a number of pre terminated pyro's connected to a central adaptable box and a box at the other end to suit the accessory that would be fitted at second fix. The pre made octopus was manufactured to suit each installation / building type on site this was secured to the ceiling / floor shuttering prior to the concrete being poured,

I have tried to find this video on the web but I've not had any success to give an insight in to how pyro was used in some cast concrete buildings, I think octopus system was used in the sixties and early seventies so if you property was built around this time it is possible this system was used
 
If a conduit installation, the conduit runs would be within the slab, installed just after the steel re-bar fixers, with the conduits tied to the re-bar. Never seen a conduit installation run on top of the slab, as for anything else, it would be out of it's installations equipotential zone, if located as you state, especially if were talking for a block of flats situation....[/QUOTE

Thats how we do it here and have done since day one, but in the 60's in the UK the steel conduit was laid on the top of the slab, the holes for the lights were formed when the slab was poured and there was a 100mm soft screed laid over the slab which covered the conduits, heating pipes etc, I dont know how they do it now, you may have never seen it but thats the way it was done all over the country and if you could bend the stuff and you could earn a fortune as most sparks were paid per flat for first fix
 
Not had time too read all the above posts,
But my house has a concrete screed floor downstairs. So essentially what you have is everything goes to the first floor void and drops down or goes up.
The central heating was surface mounted in mini trunking. I have chased this into the walls. Then into an inspection box. From here it's buried using plastic pipes wrapped in insulation within conduit. Then another inspection box at each radiator bottom for the legs.
Hope this helps
 
=Engineer54;765902]If a conduit installation, the conduit runs would be within the slab, installed just after the steel re-bar fixers, with the conduits tied to the re-bar. Never seen a conduit installation run on top of the slab, as for anything else, it would be out of it's installations equipotential zone, if located as you state, especially if were talking for a block of flats situation...

]Thats how we do it here and have done since day one, but in the 60's in the UK the steel conduit was laid on the top of the slab, the holes for the lights were formed when the slab was poured and there was a 100mm soft screed laid over the slab which covered the conduits, heating pipes etc, I dont know how they do it now, you may have never seen it but thats the way it was done all over the country and if you could bend the stuff and you could earn a fortune as most sparks were paid per flat for first fix

I'll say it again, i've never seen conduit installed this way, not in all the years i've been in the industry. It makes no sense whatsoever cost wise, or electrically!! I can only think that your talking about precast concrete slabs?? But even then, installing a metallic electrical distribution system that is outside of it's equipotential zone, again makes no sense!! And in the 60's it's unlikely that any CPC's would have been part of the wiring of that conduit system either!!
 
structural engineer comes out to the flat.

'where's the screed?'
'right there'
'have you got a chisel?'
'here'
*chisels a massive chunk out*
'yes that's screed, chase away. can you pay me £540 now?'
 
More to the point, ....what did the Structural Engineer say about your intentions to knock down walls in the apartment?? That's far more important than any screed you have over your slab floors!!! lol!!
 
he said it's fine, but the council surveyor already told me that. was a complete waste of money, basically. i guess if the building does collapse a la that dhaka primark factory at least i've got a letter saying it's not my fault - though i'd probably be crushed in the process.
 
I'll say it again, i've never seen conduit installed this way, not in all the years i've been in the industry. It makes no sense whatsoever cost wise, or electrically!! I can only think that your talking about precast concrete slabs?? But even then, installing a metallic electrical distribution system that is outside of it's equipotential zone, again makes no sense!! And in the 60's it's unlikely that any CPC's would have been part of the wiring of that conduit system either!!

I understand that you may not of seen it and you find it hard to believe, but high rise flats were wired in metalic conduit laid directly to the floor slab which was not pre cast, the lighing for the flat below was installed on the slab of the flat above, we did not install earthing conductors in the conduits as the conduit was the earthing conductor, the earth connection at the lighing point, switch or power outlet was via a cable connected to the earth lug in the box (which we had to install whilst installing the box) a soft sand screed was laid on the slab to produce the floor, this screed covered all of the conduits, I am not a liar or making this up, what I find hard to believe is the fact that you seem to want to argue when I thought the point of the forum was there to help each other, however, enough said, I know what work I carried out and how it was done on many high rise site in London, I hope there are some old buggers like me who carried out the same type of work.
 
I understand that you may not of seen it and you find it hard to believe, but high rise flats were wired in metalic conduit laid directly to the floor slab which was not pre cast, the lighing for the flat below was installed on the slab of the flat above, we did not install earthing conductors in the conduits as the conduit was the earthing conductor, the earth connection at the lighing point, switch or power outlet was via a cable connected to the earth lug in the box (which we had to install whilst installing the box) a soft sand screed was laid on the slab to produce the floor, this screed covered all of the conduits, I am not a liar or making this up, what I find hard to believe is the fact that you seem to want to argue when I thought the point of the forum was there to help each other, however, enough said, I know what work I carried out and how it was done on many high rise site in London, I hope there are some old buggers like me who carried out the same type of work.

I am one of those old buggers, but as i say, only seen conventional methods of installing conduits into slabs. ...lol!!
 
Marty203 are you sure you are not getting mixed up with maisonettes as I could then understand if their downstairs lighting conduits came from their bedrooms above. Perhaps if you where a young lad at the time you may of only worked on those parts of a large job and not remembered or recalled the conduit arrangements for the bedroom lighting which should of been cast into the slab?
 
Many years ago I can remember wiring some brand new flats in the Midlands area. We used Volex pre-wired PVC conduit which was buried in the above flat floor screed. The Volex pvc conduit fed the downstairs lighting circuits. So I would suggest be very careful, take nothing for granted. Any one remember above product? Is it still about?
 

Reply to chasing into concrete screed floors - a risk to the neighbour's lights? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top