Discuss Class 2 metal case heaters in the UK Electrical Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Reaction score
388
During an EICR the heater cases were found not connected to earth and only had 2 core cable, they do have a double insulated label on them, is this acceptable, they are fed by mcb with no rcd.
 

Attachments

  • Screenshot_20220827-095934_Gallery.jpg
    146.9 KB · Views: 18
I remember several years ago getting involved in a dispute over some De'Longhi convector heaters failing a PATest on earth bond. Like yours they were deemed to be Class II and it was argued the powder coating acted as insulation which I proved to be insufficient. Can't remember the outcome but the chances of something like this being Class II to me is somewhat optimistic.
 
Only a flash test can absolutely confirm double insulation or not in the absence of any other information
Agreed. But this will have been confirmed at the point of manufacturing, and included in the declaration of conformity.
Flash testing by an individual carrying out ISITEE is not required or recommended:

"common in PAT testing up until the IEE Code of Practice 2nd edition was published in 2001. On page 27, paragraph 10.4 it said “Dielectric strength testing is not normally carried out during in-service testing. This is normally carried out by the manufacturer on a complete appliance after assembly”. Page 48 paragraph 10.5 of the new Code of Practice 3rd edition also re-states this; thus flash testing is not normally done now."
 
No dielectric testing can be destructive and is carried out randomly at quality control by the manufacturer. A sample is taken and if it passes then all those between that and the last test are deemed okay, if it fails then all those between that and the last test are removed and further inspected.
 
Agreed. But this will have been confirmed at the point of manufacturing, and included in the declaration of conformity.
Flash testing by an individual carrying out ISITEE is not required or recommended:

"common in PAT testing up until the IEE Code of Practice 2nd edition was published in 2001. On page 27, paragraph 10.4 it said “Dielectric strength testing is not normally carried out during in-service testing. This is normally carried out by the manufacturer on a complete appliance after assembly”. Page 48 paragraph 10.5 of the new Code of Practice 3rd edition also re-states this; thus flash testing is not normally done now."
I never agreed with the flash testing when doing ISITEE when it first came in and saw it as a way of prematurely degrading equipment, the HAE advocated at one point that all hired equipment should be flash tested after every hire, I always remember the argument I had with the HAE rep / assessor at a hire shop were a couple of mates worked he was adamant it needed to be done and I was arguing the opposite and that the only time it needed to be done was after a machine was stripped down, repaired and reassembled shortly after that the HAE lost a member
The problem / challenge these days is identifying the copy / fake equipment and / or labelling and whether you should take the label as a true and accurate confirmation of it's safety
 
We used to work for a hire company and everything was flash tested. Anything the manufacturer flash tests is not sold but kept or recycled.
 

Reply to Class 2 metal case heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
269
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
597
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock