Discuss Class II Lighting in the UK Electrical Forum area at ElectriciansForums.net

M

maharg

Can anybody help?
Customer has TT system.Consumer unit(Magnuss brand ???) has 10 ways,5 of which RCD protected and 5 unprotected.
4 of the 5 unprotected circuits are lighting and these have no cpc.
Customer informed that all circuits need RCD protection and this will be done with change of CU.
Explained options of rewire or running separate 4mm cpc for lighting circuits but customer presently is not in a position for expense or upheaval of these measures.
Explained the option of class II light fittings and warning notices and the customer has opted for this.
In order to complete the work I want to purchase some inexpensive temporary pendants for the plaster ceiling roses and surface luminaires to replace the class I fittings until the customer has the funds and time to purchase more suitable fittings.
I estimated £10-£15 each to replace standard ceiling rose and pendant(£1.60) with a temporary fitting.
In the past every cheap luminaire I looked at was double insulated(possibly because they were made from plastic).Now despite 4 or 5 hours googling I cant't seem to find a cheap class II fitting anywhere.
In a lot of cases no class is given,but on those sites that specialise in double insulated lighting they are too upmarket .

Does anybody know where I can purchase cheap class II fittings.
Thanks
 
electric center do a cheap round surface class II 2D fitting. under the acel brand.
 

Reply to Class II Lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
458
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
807
Hi all! Posted on here a couple of years ago and got great advice. Have been self employed a couple of years now and always find pricing work the...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock