Discuss Coding for unfixed ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
73
Was doing an EICR and pulled out the oven to have a butchers to see if there was a connection unit or not. Hob and oven connected into same outlet, which is fine. It wasn’t fixed to the wall but, it was just sitting behind kick plate. Assuming this is due to the cable coming in surface and the surface box isn’t allowing oven to be pushed in. Would you guys code this? I’ve seen plenty of ovens plugged into a socket lying loose, just wondering what your take on it is
 
134.1.1, gotta love that reg. C3 if no signs of thermal or rodent damage. I'd be checking the loose lying patress for any damage and taking it apart for good measure to check for any thermal damage inside the socket.

If there was damage then C2 and obviously if I can get to the juicy bits without much effort (beyond moving it about) then C1.
 
134.1.1, gotta love that reg. C3 if no signs of thermal or rodent damage. I'd be checking the loose lying patress for any damage and taking it apart for good measure to check for any thermal damage inside the socket.

If there was damage then C2 and obviously if I can get to the juicy bits without much effort (beyond moving it about) then C1.
It looked fine, all cables enclosed and tight. It wasn’t trailing on the floor it was just behind where the oven sits, C3 it is
 
If the CCU has strain relief both sides, in and out, then no code. Missing strain relief, I'd probably code C3 if it seemed unlikely that it would pull apart when the cooker was moved.
 
Definitely got to consider the fact that the connections may become loose when the oven is pulled out and pushed back in. As above, it needs to have cables securely held by something.
 

Reply to Coding for unfixed ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am only asking for YOUR opinion as to what code should be given in an EICR which sees a dry wall fixing box being used for joints behind a...
Replies
4
Views
1K
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be...
Replies
40
Views
4K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
850
Hi, Just looking for a bit of advice here. I am considering swapping my existing 4 burner gas hob for a Bosch induction one. I am not proposing...
Replies
10
Views
5K
Hey, question for the group on grounding when using MC cable and metal boxes.... Situation: Enclosed a carport and turned it into a garage. I'm...
Replies
1
Views
883

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock