A customer I've been doing work for since I went self employed is in the process of selling their restaurant and they're needing retrospective planning permission for some dividing walls they had built to split up the restaurant/bar. They need an electrical certificate for extra emergency lights and extra sockets installed. What cert would I need to issue? The work was done before I was on the scene.
 
Can test as much or as little. There will be a section on front that you fill in titled something along the lines of: extent of installation covered by this certificate
 
you have a chioce. either a condition report on the whole installation, or just for the works specified in your OP. but be sure to note it on the cert. the extent of the works covered by your report.
 
but the fool was once the highest paid in the king;s court!.
 
Sweet. I maybe worded the question wrong, I knew it would be a condition report but wasn't sure on the extent of how much I needed to test!

As the report is for a retrospective planning application, then surely the extent of the report needs to be agreed with the customer and the building control officer ?
 
nowt wrong with a fart. toally natural, no added flavours. best appreciated when you pull the bed covers over 'er indoors' head.
 
A customer I've been doing work for since I went self employed is in the process of selling their restaurant and they're needing retrospective planning permission for some dividing walls they had built to split up the restaurant/bar. They need an electrical certificate for extra emergency lights and extra sockets installed. What cert would I need to issue? The work was done before I was on the scene.
Slightly confused here, firstly you are saying "Extra lights and sockets" then work was done before on scene, which is it? if the work has been done then I would tell your customer to get a certificate from the electrician who did the initial works, if that isn't possible then as Kate rightly pointed out you carry out a EICR.

Now if you are talking about "Extra works" as in new, then you will need to either supply a MW if you have used existing circuitry, or a EIC if you install new circuitry, HTHs.
 

Reply to Completion certificate in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top