Search the forum,

Discuss Confirming earth bonding continuity when cannot isolate supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
6
Hi, just wondering how other sparks, go about confirming main earth bonding continuity when supply cannot be isolated, ze and pfc can be enquired wich is fine but what happens if you cant disconnect main bonding earth, is previous test results good enough to confirm?visual checks good enough? can this be a limitation on a condition report or not? And how would we overcome this if it was an initial verification or a minor works, just wondering what's the minimum acceptable to tick those boxes.

Theres so many variables it's hard to gauge what would be acceptable to tick those boxes on test certs.

Help much appreciated

Many thanks
 
You can’t simply say that the main bonding cannot be verified for initial verification for new work or additions as per regulation 132.16.
 
You can normally confirm the Zs and PFC by measurement without isolating the supply.

Of course that assumes you can access the terminals safely without isolation, and that is something you should consider very carefully before attempting it. Many panels and switch-fuses have mechanical interlocks to avoid being opened in the energised position for very obvious safety reasons, and even removing covers that might expose live busbars is something you really ought not to do live in case of accidental contact.

What you cannot do without isolation is confirm Ze as that requiers the supply earth to be isolated from the installation to measure without any parallel earth paths via bonding to service pipes, structural parts, lightning conductors, etc.
 
is previous test results good enough to confirm?visual checks good enough? can this be a limitation on a condition report or not?

Who said that?
 
Not sure I understand what you mean?
I’m simply saying that for initial verification you cannot state that the bonding conductors haven’t been verified as adequate for the new or altered works.
The regulation is in fundamental principles of bs7671
 
A bit more background on why it can't be isolated, and the size/complexity would help.

If you have access to the incoming supply point somewhere and the earth is routed in some non-obvious way, you could always use a wander lead and confirm it is at the expected sort on resistance (guess X metres route length, guess CSA at 16mm or whatever, look up table and compute)
 
Last edited:
Hi guys help appreciated, so the installation is an events venue, two massive transformers on site that feed two big switchboards, we dont have authority to start opening up the switchboards even if we could isolate, , is it acceptable to start disconnecting main incoming earths from buss bars etc, it just seems very intrusive work on a big install for conditon report, and the same stands for initial verification, I wouldn't have thought every time we add a 20amp radial circuit off a sub main board, we have to isolate the whole venue and strip down a switchboard. This is why I would have to inquire ze and pfc wich helps me there but then it's the ticking of main earth and main bond "connection/continuity varified" the way I see it it is asking connection or continuity verified so would previous results and a visual be enough to tick without a lim as like you say we cannot lim on initial verification How would you guys go about those situations, condition report and initial verification.

I feel this is a common situation and people would just have a quick look and give it a tick but I like to be as furough as possible and wonder if I'm missing a trick.
 
Hi guys help appreciated, so the installation is an events venue, two massive transformers on site that feed two big switchboards, we dont have authority to start opening up the switchboards even if we could isolate, , is it acceptable to start disconnecting main incoming earths from buss bars etc, it just seems very intrusive work on a big install for conditon report, and the same stands for initial verification, I wouldn't have thought every time we add a 20amp radial circuit off a sub main board, we have to isolate the whole venue and strip down a switchboard. This is why I would have to inquire ze and pfc wich helps me there but then it's the ticking of main earth and main bond "connection/continuity varified" the way I see it it is asking connection or continuity verified so would previous results and a visual be enough to tick without a lim as like you say we cannot lim on initial verification How would you guys go about those situations, condition report and initial verification.

I feel this is a common situation and people would just have a quick look and give it a tick but I like to be as furough as possible and wonder if I'm missing a trick.
Course you wouldn't, that's what Zs@DB is for.
 
Zs at db on the test shchedual yes but that doesnt satisfy the ze and PFC at origin section on the top sheet for an initial verification does it? These are two different tests
I believe it would. The purpose is to check that the fault path is unbroken no? (Values will of course be higher due to length)

Came across this; https://---------------/forums/forum/messageview.cfm?catid=205&threadid=26810
 
I believe it would. The purpose is to check that the fault path is unbroken no? (Values will of course be higher due to length)

Came across this; Electrical Blog - Electrical Advice | Free Electricians Advice Forum - https://electriciansforums.co.uk/forums/forum/messageview.cfm?catid=205&threadid=26810
Yes but ze needs to be done at origin with earth disconnected, by just copying your zs at db result this includes parallel earth paths, and also would be from db not origin , so I would have thought we enquire everytime, and then visual check for earth and main bond connection. Cant think of any other way to do it without isolation and very intrusive work on a switchboard? Thanks for your reply, notsure what the link was supposed to show me... was just a webpage with no thread...
 
Not absolutely foolproof due to parallel earths etc. but an approximation closer than no test at all is from MET wander lead to pipe in proximity of clamp if a low reading >1 ohm then there is some evidence their is continuity. What do others think?
 
There is every chance there is no earthing conductor from the transformer anyway and that your main earth bars are bonded to the supply neutral.
 
If it is a venue with its own transformers than the supply Ze is going to be quite low and if you know the approx length and type of the sub-main cable to your board you could be fairly confident that a Zs measured there is in close enough agreement to establish the supply arrangement is sound.

Also it probably has the installation & test results from before and if it appears to be sound and well maintained than you would have no reason to doubt it unless the Zs looked oddly high.
 
Yes all this is correct , so I would have thought visual would be fine for earth connection tick box, and ze and pfc just put down enquired values? Or would you feel comfortable writing a zs at sub main value in the ze section? As enquiry is acceptable for ze and pfc I think I would just put enquired values, but obviously safe in the knowledge we have good earths from visual and like you say previous install test results. You have confirmed in similar thinking to me and dont think theres any other way around it. Thanks for everyones input!
 

Reply to Confirming earth bonding continuity when cannot isolate supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock