Search the forum,

Discuss Continuity test after Ring Circuit in the UK Electrical Forum area at ElectriciansForums.net

Status
Not open for further replies.
When undertaking any test whether electrical or not you must understand how the test equipment operates and how to interpret the results it gives you, you do not understand either of these from the questions you are asking.
 
Last edited:
A few more questions on this please Tim:
  • Can I remove USB sockets with 32amp junction boxes for the purposes of the IR test?
  • Do FCU's that are on the ring and not a spur need to be removed? The neon is on load and can be switched off
  • If we have continuity as part of earlier tests, when doing the IR test for L and E (or the other conductors), does it matter which leg of the ring you use the L and E from? I assume not but was mindful of the other end of the leg hanging mid air at this point:
View attachment 98571
- If there are failures, we can use the halving method and I can gradually increase the working leg of the ring to see where the failure appears. At this point, I could either replace the cable or convert the ring into two radials powered by a 20amp breaker. Is that a valid approach?
I would really appreciate any direction that could be provided on the above please.
Thanks in advance
 
Is this related to your other threads.
 
As to your fault, my best guess is a nail used for capping has missed and has damaged a cable. Or a screw at a socket has caught the Neutral.
Breaking down the ring, with an IR tester is the only way to proceed I'm afraid.
This is precisely what happened! I wanted to share my experiences.
I used my newly purchased Megger MFT to run the continuity, crossover tests and then the insulation tests. The IR test failed.
I halved the ring and identified the good and bad legs. I then kept adding sockets to the good leg until it turned bad. Hope that's making sense...

That's when I noticed that a neutral wire was nicked behind an electrical screw of the face plate. The Megger MFT and halving method made this light work and I enjoyed the experience of troubleshooting it.

  • I didn't remove USB sockets and they are fine. I started with a 240v IR test and then increased it to 500v. Although, the latter probably wasn't required as fault showed on the 240v test.
  • The FCU on ring remained in placed with switch in off position
  • I was able to use either L or N as there was continuity all the way around the Ring before I started the IR test.


My only question is why this fault only caused the RCD to trip under load and a certain amount of load i.e. phone charger plugged in seemed okay but the hammer drill would immediately trip it?

Thanks for your support with this.
 
I'm glad you found the issue.
My only question is why this fault only caused the RCD to trip under load and a certain amount of load i.e. phone charger plugged in seemed okay but the hammer drill would immediately trip it?

An RCD works essentially on the principle that what goes out must come back, and if more than a certain amount is 'missing' it trips.
So no load at all, nothing, goes out, nothing goes back.
A phone charger is a very low load, and the "missing" amount wouldn't be high enough.
A drill pulls enough current that enough goes the 'wrong way back' (via the cpc/earth ) that the RCD would have an aha moment.
 
As timhoward mentions, it is load related with an imbalance, which might be telling you your drill is on the way out. There is a lot of information regarding how RCD's Work online with pictures too.
 
Status
Not open for further replies.

Reply to Continuity test after Ring Circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock