Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and would be incredibly grateful of any guidance or help anyone could offer. its for a design project and i'd like to know if i'm doing something wrong somewhere. here are the details of the circuit etc...
garage board Zdb = 0.22 ohms
ring final circuit wired in 2.5mm²/1.5mm² twin and cpc
circuit length = 30 meters
protective device B32 61009-1 RCBO
2.5/1.5 T+E milliohms per meter = 19.51
temp correct factor = 1.2
K=115
my calculations are as follows; (figures rounded up to two decimal places)
r1 = 7.41 x 30 x 1.2 ÷ 1000 = 0.27 ohms
r2= 12.10 x 30 x 1.2 ÷ 1000 = 0.44 ohms
(R1+R2) for ring final circuit = r1+r2÷4 = 0.27+0.44÷4 = 0.18 ohms (R1+R2)= 0.18 ohms
Zs= Zdb+(R1+R2) 0.22+0.18=0.4 Zs = 0.4 ohms
Ipefc= Uo x Cmax ÷ Zs = 230x1.1÷0.4 = 632.5 amps Ipefc= 632.5 amps
heres where i think im going wrong...
using log graph in bs7671 fig 3A4 disconnection time for BSEN61009-1 B32 with fault current of 632.5amps = 0.1 sec
632.5 x 632.5 = 400,056.25
400,056.25 x 0.1 = 40,005.625
square root of 40,005.625 = 200.014
200.014 ÷ 115 = 1.73 mm²
So S is equal to 1.73 mm² which is the CSA of my CPC which means that my simple 30 meter ring final circuit wired in 2.5/1.5 twin and cpc has now got to be changed to 2.5mm² singles which will then comply with 543.1.4 and table 54.7 AND the adiabatic equation.... OR..... because my fault current is in excess of those causing instantaneous operation of protective device, i.e less than 0.1 second, do i need to start comparing I2t and K2S2 energy let through data etc? i'm sure im going wrong somewhere and would be incredibly grateful if anyone could shed some light or point me off in the right direction with this.
thank you again to anyone that has taken the time to read this.
garage board Zdb = 0.22 ohms
ring final circuit wired in 2.5mm²/1.5mm² twin and cpc
circuit length = 30 meters
protective device B32 61009-1 RCBO
2.5/1.5 T+E milliohms per meter = 19.51
temp correct factor = 1.2
K=115
my calculations are as follows; (figures rounded up to two decimal places)
r1 = 7.41 x 30 x 1.2 ÷ 1000 = 0.27 ohms
r2= 12.10 x 30 x 1.2 ÷ 1000 = 0.44 ohms
(R1+R2) for ring final circuit = r1+r2÷4 = 0.27+0.44÷4 = 0.18 ohms (R1+R2)= 0.18 ohms
Zs= Zdb+(R1+R2) 0.22+0.18=0.4 Zs = 0.4 ohms
Ipefc= Uo x Cmax ÷ Zs = 230x1.1÷0.4 = 632.5 amps Ipefc= 632.5 amps
heres where i think im going wrong...
using log graph in bs7671 fig 3A4 disconnection time for BSEN61009-1 B32 with fault current of 632.5amps = 0.1 sec
632.5 x 632.5 = 400,056.25
400,056.25 x 0.1 = 40,005.625
square root of 40,005.625 = 200.014
200.014 ÷ 115 = 1.73 mm²
So S is equal to 1.73 mm² which is the CSA of my CPC which means that my simple 30 meter ring final circuit wired in 2.5/1.5 twin and cpc has now got to be changed to 2.5mm² singles which will then comply with 543.1.4 and table 54.7 AND the adiabatic equation.... OR..... because my fault current is in excess of those causing instantaneous operation of protective device, i.e less than 0.1 second, do i need to start comparing I2t and K2S2 energy let through data etc? i'm sure im going wrong somewhere and would be incredibly grateful if anyone could shed some light or point me off in the right direction with this.
thank you again to anyone that has taken the time to read this.