Currently reading:
Cpc connection wylex

Discuss Cpc connection wylex in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 
Could you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?

i.e. Ignore the switch's through-CPC connection and the box's terminal strip completely.

EDIT: Also you could use a nylock nut if concerned about it coming loose.
Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheap
 
Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheap
Could you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:

https://www.NoLinkingToThis/p/ced-4-way-earth-block/12386

You might need to have nuts on top and use countersunk heads coming through from the back to is fixes flush though.
 
Could you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:

https://www.NoLinkingToThis/p/ced-4-way-earth-block/12386

You might need to have nuts on top and use countersunk heads coming through from the back to is fixes flush though.
That’s a good option it’s a shame I have fifteen to do of these
 

Attachments

  • F4409C8C-B1A3-4561-98BF-31944FDE34FB.jpeg
    165.9 KB · Views: 22
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
I will get over with unnecessary work as the switch fuse by wylex is very poorly designed
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
i still think there are a lot of these installed where the installer thinks the cpc connection is common to the enclosure
 
It really is a terrible design putting in such a small separate terminal however Wylex may have calculated the worst scenario for fault protection and that a 6.0 would satisfy. I would email them.
 
They are rubbish considering the price of them, as usual the designer has never had to fit one or they would have noticed the massive cock up with the earth terminal!
The last one of those I fitted I ran the SWA cpc to the earth banjo bolt and lugged the 16mm outgoing on that as well. As stated above an earth nut would probably be quicker!
Sy
 

Reply to Cpc connection wylex in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock