CU Replacement - Upstairs and Downstairs Rings Connected

Discuss CU Replacement - Upstairs and Downstairs Rings Connected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

SW1970

Hi, newbie here. Done a domestic PIR and Consumer Unit replacement is required (damaged, lighting circuit not earthed or RCDd, plus other reasons). However, another finding was that the upstairs and downstairs ring final circuits are connected (currently installed as the 2 live cables going into the circuit breaker).

Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).

After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.

Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).

I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?

Many thanks
SW
 
Hi, CU replacement is required anyway because the existing one is damaged, but circuits are:

Cooker
Downstairs lights
Upstairs lights
Garage lights
Garage sockets
Upstairs and downstairs sockets
Utility room sockets

Cheers
SW
 
Topquark - could be. House is 1963 build. Utility room is an extension so that would explain why it's on a separate circuit.
 
As your readings are all pretty much identical my first guess would be only one ring. How many cores do you have back at the CU?


(currently installed as the 2 live cables going into the circuit breaker).
SW
Same question as topquark,
I dont quite get what that description is suggesting
 
Two 2.5mm2 cores going into the MCB labelled sockets upstairs and downstairs. So if it is a single ring installation, ok to proceed with CU replacement and identify the segregation deviation from BS7671? Cheers, SW
 
Two 2.5mm2 cores going into the MCB labelled sockets upstairs and downstairs. So if it is a single ring installation, ok to proceed with CU replacement and identify the segregation deviation from BS7671? Cheers, SW

If you have 2 other socket circuits, then I wouldn't even be concerned, I don't see a safety issue on a nuisance trip?

The
'departures' box is strictly relating to your work only and if you did feel the need to make a note, it should be recorded in the 'comments on the existing installation' box.
 
Well you have segregation to a certain level because of the seperate utility sockets
An household ring and a kitchen or utility ring where most of the heavy loads are sited would satisy the segregation of circuits requirement in my opinion
 
or aqs inspector clusseau would say " c'est que ces't votre minky"
 
Hi, newbie here. Done a domestic PIR and Consumer Unit replacement is required (damaged, lighting circuit not earthed or RCDd, plus other reasons). However, another finding was that the upstairs and downstairs ring final circuits are connected (currently installed as the 2 live cables going into the circuit breaker).

Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).

After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.

Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).

I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?

Many thanks
SW

Have you done r1, rn, and r2 end to end, if you have, and r1, and rn are the same, and r2 is about 1.67 times the value of either r1 or rn then you have one circuit, R1+R2 at every outlet will then show up any spurs, reverse polarity, interconnections (ring within a ring etc),and any faults like loose connections.

Cheers.......Howard
 

Reply to CU Replacement - Upstairs and Downstairs Rings Connected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top