Search the forum,

Discuss CU Replacement - Upstairs and Downstairs Rings Connected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

SW1970

Hi, newbie here. Done a domestic PIR and Consumer Unit replacement is required (damaged, lighting circuit not earthed or RCDd, plus other reasons). However, another finding was that the upstairs and downstairs ring final circuits are connected (currently installed as the 2 live cables going into the circuit breaker).

Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).

After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.

Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).

I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?

Many thanks
SW
 
Hi, CU replacement is required anyway because the existing one is damaged, but circuits are:

Cooker
Downstairs lights
Upstairs lights
Garage lights
Garage sockets
Upstairs and downstairs sockets
Utility room sockets

Cheers
SW
 
Topquark - could be. House is 1963 build. Utility room is an extension so that would explain why it's on a separate circuit.
 
As your readings are all pretty much identical my first guess would be only one ring. How many cores do you have back at the CU?


(currently installed as the 2 live cables going into the circuit breaker).
SW
Same question as topquark,
I dont quite get what that description is suggesting
 
Two 2.5mm2 cores going into the MCB labelled sockets upstairs and downstairs. So if it is a single ring installation, ok to proceed with CU replacement and identify the segregation deviation from BS7671? Cheers, SW
 

Reply to CU Replacement - Upstairs and Downstairs Rings Connected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K
Hi All Let me start by saying I have my 2365 level 3 but never worked in the industry so my knowledge is limited. My partner and I recently...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock