Discuss Discrimination Study in the Industrial Electricians' Talk area at ElectriciansForums.net

timbobelfast

-
Arms
Reaction score
223
Can anybody explain the discrimination overlaps in the attached protection study?

For example, a Live to earth fault in the downstream OCPD and how this may play out.

I know the current settings are not ideal, but this is a legacy issue restricted by cable sizes etc!
 

Attachments

  • Export_Selectivity_Study.pdf
    110 KB · Views: 22
Can anybody explain the discrimination overlaps in the attached protection study?

For example, a Live to earth fault in the downstream OCPD and how this may play out.

I know the current settings are not ideal, but this is a legacy issue restricted by cable sizes etc!
I think "very poorly" is how it would play out!

But the plots don't quite look right to me. For example:
  • The HV fuses would be transformed from 100A at 6.6kV to 400V (presumably) at 1650A equivalent, but the plot shows them coming in at around the 10kA point.
  • The first ACB is set to 1440A but seems to be starting its trip region around 8kA
  • The 800A BS88 fuses at around 4kA
  • The second ACB seem to trip at roughly the same threshold, but has a very aggressive time/current setting, probably an attempt at selectivity
It might be the log-scale plot is just out by some factor, as relative to each other the plots look believable.

What is not clear though is the ACB let-through and if they can possibly stop the upstream fuses from going, as most mechanical breakers take a few milliseconds to initiate opening and that normally lets through a whole lot more energy than a HRC fuse might for the same sort of conditions.

Same applies for the ACBs for any down-stream fuses, though the #1 seems to have been set with a bit of a delay to try and remain selective with the down-stream 800A fuses, but as you can see on the plot (ignoring and scale errors for now) the brown and blue curves cross each other at multiple points so there are various fault currents that would lead to having, or not having, selectivity there.
 
Last edited:
If the curves are to believed, and the fault currents to scale, then downstream of the Wallascetown ACB should be OK, it appears to disconnect before any of the others, but it is not clear what happens in the region below 100ms or so. It might well have too much let-through.

Otherwise the bad news is the HV fuses are probably going to go before anything else! At least for faults above the 3kA-ish sort of range (guessing the horizontal scale).

Hopefully @Julie. will be along soon, this is her sort of area!
 

Reply to Discrimination Study in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
612
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
794
I have seen recent changes that require (most) EV chargers and solar systems to be fitted with a type B RCCD. I work with power semiconductors...
Replies
9
Views
1K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock