Are you referring to Mr. Eddie currents ?Right I’m going to pi$$ on everyone’s parade.
If the CPC is run through steel conduit you have circulating currents and reactance to take in to account. A single conductor through a magnetic conductive trunk is a NoNo! Plastic, aluminium or stainless steel protection is OK, but not plain conduit!
Right I’m going to pi$$ on everyone’s parade.
If the CPC is run through steel conduit you have circulating currents and reactance to take in to account. A single conductor through a magnetic conductive trunk is a NoNo! Plastic, aluminium or stainless steel protection is OK, but not plain conduit!
That makes sense.Reply to #14
No it doesn’t because the lines of magnetic flux in the conduit will be at 90°to the CPC current.