We have been asked to carry out some linking up eart bars on 5 blocks of flats, they want the CPC running in metal conduit, where I think that a CPC can be clipped direct, anyone know the answer and possible reg number.
 
If the job's specification calls for earth cables to be run in metallic conduit, then that is exactly what you provide the client. It doesn't matter a jot, what you think, or how you want to install these earth cables, the job's Specification is what you work too!! It's the same on all projects, where the Specification can and often does over rule Regulations, provided is of a higher order!!
 
Right I’m going to pi$$ on everyone’s parade.

If the CPC is run through steel conduit you have circulating currents and reactance to take in to account. A single conductor through a magnetic conductive trunk is a NoNo! Plastic, aluminium or stainless steel protection is OK, but not plain conduit!
 
but, tony, surely the only time a current will flow is during a fault condition, for a short duration till the ocpd operates.
 
Right I’m going to pi$$ on everyone’s parade.

If the CPC is run through steel conduit you have circulating currents and reactance to take in to account. A single conductor through a magnetic conductive trunk is a NoNo! Plastic, aluminium or stainless steel protection is OK, but not plain conduit!
Are you referring to Mr. Eddie currents ?
 

Reply to Does a CPC require mechanical Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
584
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock