Does a CU swap require a full initial verification on all circuits before it can be energised?

Discuss Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Surely that is referring to the design process.
132.16 states: "No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including the distributor, will be adequate for the altered circumstances
 
Ah, right. The electrician refused to do the testing based on the C3. Said it failed outright.

Periodic inspection and testing every 12 months.

I admit it's a weird one. Just my own pondering whether the installer could have given permission to energize.
But that periodic testing is only as good as the day it's tested, and the eicr does not apply once the board has been changed. Much like the mot on your car. Except changing the board is like taking every single screw and bolt out of your car, putting them back in and not getting it checked. He couldn't give permission to energise whilst still following regulation.
 
Last edited:
But that periodic testing is only as good as the day it's tested, and the eicr does not apply once the board has been changed. Much like the mot on your car. Except changing the board is like taking every single screw and bolt out of your car, putting them back in and not getting it checked. He couldn't give permission to energise whilst still following regulation.

Unless he inspected and tested. Which he could have done. But didn't. (I still find no regulation supporting your view mind.)
 
What was this C3 and was this C3 from a previous EICR.

The C3 was a 70-90mm gap between the existing conduit and the board. Planned to be sorted with boxing in later and grommets. Risk assessment done expected very low risk from the position of the board. Could not physically cause or contribute to an accident short of sticking a fork in it.
 
Unless he inspected and tested. Which he could have done. But didn't. (I still find no regulation supporting your view mind.)
You find no regulation that says you can't energise a circuit without testing being completed? I wont attempt to justify what I said, as I know i am correct. Scary to think anyone would consider energising anything without confirming its Sage
 

Reply to Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock