New build as in new room in the loft.
Or are you saying the loft was already converted?
Nope, I think the suggestion is the designer must divide the circuits across RCD's, so that any anticipated earth leakage would be limited to 30% of the tripping current for the RCD, i.e. 10mA for 30mA RCD. So consideration of the appliances and loads connected to said RCD. Kitchen appliances and IT equipment come to mind.
Westy proceeds me. See why its important to read & comment on the draft. You've got 3 days left.
Did the loft originally have sockets and lights?Was a loft, now 2 rooms
It is a new Reg in the 18th Ed draft, 10% of the rated residual operating current of the device.I thought it was 25% so 7.5mA.
I haven't got regs book in front of me so I may be wrong
Did the loft originally have sockets and lights?
Were they on separate circuits?
Were the separate circuits protected by a single RCD?
It is a new Reg in the 18th Ed draft, 10% of the rated residual operating current of the device.
I was referring to #30.Can you please expand on that?
I thought it was 25% so 7.5mA.
I haven't got regs book in front of me so I may be wrong
It is a new Reg in the 18th Ed draft, 10% of the rated residual operating current of the device.
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.
So if we can just slap in single up front RCD boards, what is the point of the reg in question AND why did we all start putting in dual RCD boards
Just wondering ?
I am only quoting a rule of thumb I believe may be quoted in a commentary/guide book which is what Paignton Pete has probably seen and stuck in his mind. 25% equates to 7.5ma for a 30ma device and it does ring a bell in my head that this should be used as a basis for circuit design. It may have some substance with the proposed 18th Ed quoting 30%.Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
Okay this is bugging me so if you have a 16th Ed copy with Section 607 in it check out Regulation 607-02-03 there you will find it.Thanks for that westward. I've checked your post #30. That's interesting to know.
I've now got my books out( 17th edition that is) and I still cannot find where I've think I've seen 25% of rated residual current as a design guidance. Therefore a 30mA rcd should be designed with7.5mA as its max.
I know I've seen it somewhere.
I'm wandering where the 30% 9mA came from.
The aim here is to keep the currents at a happy level to prevent unwanted tripping, ideally an rcd/rcbo should trip under fault conditions and not excessive leakage when there is no fault. By quoting a percentage level you allow some leeway for further accumulated current and all should be good. Design a circuit where levels are excessive then any further accumulated current may result in unwanted tripping.Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.