O

Octopus

Been at a place today.......... brand new loft conversion.......... so an additional CU has been fitted for the lights and sockets ......................

Thinking specifically about 314.2 :

Kate CU.jpg


I would say that it doesn't............

Opinions please

and more to the point, this conversion probably cost about £45k so using RCBO's wouldn't have been noticed................

The last one I saw was where a new single RCD board had been used for the entire house and loft conversion.............. why do people do this?
 
Because your saying that if the RCD trips then the power and lighting circuits will go off in the loft.Going on that principle then when a dual RCD board trips one of its RCD's then 4-5 circuits go off.Obviously this practice is still accepted as being ok otherwise the powers that be will have told us to fit RCBO's to everything as standard.
 
But is it not that you put downstairs lights on the RCD with the upstairs sockets and visa versa. Enabling that if a trip fault occurs on 1 Circuit you still have lighting ability via the sockets in that area coming from the other RCD, which voids the dual RCD argument.
 
I hope thats not your safe isolation Murdoch lol

What I was doing was in the main house - so not my "safe isolation".

FWIW the "other" CU was an older MK - with a 30Ma main switch!

If it was me I would have taken one of the other lighting circuits out of the old board and put it in the new board, then placed the new lighting circuit in the old board!
 
I was taking mick m8 lol im still training and learning.
But agree on the point of rcbo's as it was a new loft conversion so wouldn't of cost much. Im not to keen on the fact if a fault occurs they will loose both circuits in the loft so I would of either separated them or fitted rcbo's
 
OK, I agree that RCBOs all round is 'best' and minimising inconvenience is a good thing. However, I think that the problem of being plunged into darkness is over-stated. Where I am, you're much more likely to have a power cut than an RCD trip. So, if darkness was a major safety issue, we would be installing emergency lighting to all rooms in domestic premises.
 
Because unless you are going to argue that the Regulation requires every circuit to be individually RCD protected then it doesn't hold water. And that certainly isn't what is demanded by BS7671. Minimising inconvenience is a matter for a risk assessment - nowhere is it suggested that all possible inconvenience must be eradicated. So whilst you are entitled to your own interpretation of the Regulation I wouldn't agree with such an interpretation. If that's what JPEL/64 had wanted then presumably that's what they would have written.
 
What I was doing was in the main house - so not my "safe isolation".

FWIW the "other" CU was an older MK - with a 30Ma main switch!

If it was me I would have taken one of the other lighting circuits out of the old board and put it in the new board, then placed the new lighting circuit in the old board!

Is the “Other CU” with RCD as main switch supplying the new loft cu? No discrimination if that is the case?
 
If I was doing the installation for the loft conversion, I would of considered 314 and installed RCBO's.

In this install, if the RCD trips, and the occupier gets up in the middle of the night to investigate and trips over his bed pan, 'cos he's got no bed side light or room light, the installer has not done all he/she can to 'avoid danger & minimise inconvenience etc'.

So I agree with Murdoch IMO.
 
As already stated it's a non issue.
If the end user loses the loft conversion electrics he can run a lead from elsewhere until it's fixed. If it's just nuisance tripped then the rest of the house is still on so he can see to reset.
 
As already stated it's a non issue.
If the end user loses the loft conversion electrics he can run a lead from elsewhere until it's fixed. If it's just nuisance tripped then the rest of the house is still on so he can see to reset.

Not easily done in the middle of the night, or if your elderly or infirmed or just a little bit squiffy. Not really a good design, if you have to faff around with extension leads (not everyone has one), when a couple of RCBO's is a simple but easy fix?
 
You are of course entitled to take that view.....but really your objection makes no sense. If it was installed on 2x RCBO's and the lighting one tripped during the night, and your elderly /infirm/squiffy type does not have a light plugged in or cant reach it then your RCBO has not improved their safety one bit.....Of course RCBO's are always preferable but to suggest this is non compliant with just two circuits on a separate RCD and the rest of the house unaffected is incorrect IMO.
A job I did last week involved 4 new circuits for kitchen equipment which I supplied from a 4 way DB with an RCD main switch, the rest of the existing installation is split over two RCD's on the existing DB. I have an NICEIC visit next month and he'll probably see this job. I'll let you know if he pulls it up as non compliant.
 
You are of course entitled to take that view.....but really your objection makes no sense. If it was installed on 2x RCBO's and the lighting one tripped during the night, and your elderly /infirm/squiffy type does not have a light plugged in or cant reach it then your RCBO has not improved their safety one bit.....Of course RCBO's are always preferable but to suggest this is non compliant with just two circuits on a separate RCD and the rest of the house unaffected is incorrect IMO.
A job I did last week involved 4 new circuits for kitchen equipment which I supplied from a 4 way DB with an RCD main switch, the rest of the existing installation is split over two RCD's on the existing DB. I have an NICEIC visit next month and he'll probably see this job. I'll let you know if he pulls it up as non compliant.


Well, I seem to recall someone on this forum arguing that a dual RCD set up, was non compliance with 314. I think that's a bit extreme. What someone does with an installation after you've installed it, you have no control over. But in the example given here, at least having two separate RCBO's would give some scope.

In the example you've given, a loss of complete power to a kitchen, is unlikely to cause danger as suggested in 314, although it may well cause inconvenience. However, the control of both lighting & power for a bedroom at night by one RCD, could cause danger, dependant on the end user (when I designed this, did I do all that was reasonably practicable).

You may be aware that the draft for the 18th, will make more demand of the designer to consider unwanted tripping, (proposed) reg 531.3.2. Limiting down stream current to 30% of the RCD rating. So perhaps you kitchen design may not comply with the 18th?
 
Well, I seem to recall someone on this forum arguing that a dual RCD set up, was non compliance with 314. I think that's a bit extreme. What someone does with an installation after you've installed it, you have no control over. But in the example given here, at least having two separate RCBO's would give some scope.

In the example you've given, a loss of complete power to a kitchen, is unlikely to cause danger as suggested in 314, although it may well cause inconvenience. However, the control of both lighting & power for a bedroom at night by one RCD, could cause danger, dependant on the end user (when I designed this, did I do all that was reasonably practicable).

You may be aware that the draft for the 18th, will make more demand of the designer to consider unwanted tripping, (proposed) reg 531.3.2. Limiting down stream current to 30% of the RCD rating. So perhaps you kitchen design may not comply with the 18th?

I am not aware of those proposals, are you saying it is proposed that a 63a RCD would be restricted to a load of 21a?.....then presumably a 32a RCBO would be restricted to under 11a?
So a 10kw shower would need a minimum 135a RCBO ?....Sorry if I'm having a blonde moment but that just doesn't make any sense.
 
Last edited by a moderator:
That's surely relating to the residual earth leakage current, no? So they are saying that if you have appliances that have a heavy leakage then a 100ma RCD will have to be provided up from 30ma or division of leakages attempted?
 
Correct, the accumulated leakage of upstream circuit/s from an rcd should not exceed 30% of the rcds rated residual current. So for an rcbo it applies to the connected circuit, for a dual rcd board the accumulated conductor current and/or leakage applies to the sum of circuits protected by each rcd. So for 30ma that is 9ma if my math is correct.
 
That's surely relating to the residual earth leakage current, no? So they are saying that if you have appliances that have a heavy leakage then a 100ma RCD will have to be provided up from 30ma or division of leakages attempted?

Nope, I think the suggestion is the designer must divide the circuits across RCD's, so that any anticipated earth leakage would be limited to 30% of the tripping current for the RCD, i.e. 10mA for 30mA RCD. So consideration of the appliances and loads connected to said RCD. Kitchen appliances and IT equipment come to mind.

Westy proceeds me. See why its important to read & comment on the draft. You've got 3 days left.
 
So RCBO boards would effectively negate leakage from other areas on other circuits -
Nope, I think the suggestion is the designer must divide the circuits across RCD's, so that any anticipated earth leakage would be limited to 30% of the tripping current for the RCD, i.e. 10mA for 30mA RCD. So consideration of the appliances and loads connected to said RCD. Kitchen appliances and IT equipment come to mind.

Westy proceeds me. See why its important to read & comment on the draft. You've got 3 days left.
Your kitchen leakage would be on that RCBO and your IT leakage on the downstairs ring or radial.
 
With rcbos you will not get accumulated currents from other circuits but rcbos are lawless things. It suggests correct division of circuits to avoid unwanted tripping so for example if you install a ring final circuit with ten points of utilization is there a likelihood accumulated leakage currents of connected appliances may cause unwanted tripping, if yes then two ring final circuits with five on each may be a better option.
 
That makes more sense. It would not be an unreasonable proposal to design a low potential earth leakage into an RCD protected circuit.
Cue amended forms and earth leakage measurements on all RCD protected circuits.
 
I clamped my own house the other day. PC running, few led lights on, tv on, appliance turned on but not running. Clamp meter's a cheap en, but I had 14mA leakage. But I've have that split across RCD & RCBO's. Went to a job in the afternoon, semi with 1 x lighting, 1 x RFC & electric cooker. 9mA eath leakage.
 
So if we can just slap in single up front RCD boards, what is the point of the reg in question AND why did we all start putting in dual RCD boards

Just wondering ?
 
Nope, I think the suggestion is the designer must divide the circuits across RCD's, so that any anticipated earth leakage would be limited to 30% of the tripping current for the RCD, i.e. 10mA for 30mA RCD. So consideration of the appliances and loads connected to said RCD. Kitchen appliances and IT equipment come to mind.

Westy proceeds me. See why its important to read & comment on the draft. You've got 3 days left.

I thought it was 25% so 7.5mA.
I haven't got regs book in front of me so I may be wrong
 

Reply to Does this comply with 314? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
568
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
785
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
969
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top