Search the forum,

Discuss Double insulated singles on 2 way switching in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

stimpy

As per title, d.I singles or 'insulated and sheathed singles' with no earth within cable and not run alongside any earths. What is the current view on these within an EICR?

There are earths at all the accessory and light points but i was always taught that every cable needed a cpc on the basis that if it did get cut then something would trip......

TIA
 
I don't think there's a problem. Can't think of a regulation requiring a cpc in every cable. The cpc may add a little extra safety to a cable in some circumstances, but that's not what it's there for.

After all, appliances can have flexible cables without a cpc and they're more likely to become damaged than fixed wiring. Plus, of course, meter tails don't have a cpc.
 
543.6.1 may apply here. It's not a situation I have encountered before nor have heard of though. I can't imagine how the CPC is run if not with the live conductors or how you have verified this one way or the other.
 
As a design now it is not a good arrangement (and would be difficult to arrange).
I would assume this is in relation to two wire two way switching of lighting where singles have been used to supply the switch and feed the light.
If the single core is adequately protected from mechanical damage and has been in place for a long time then there should be no significant risk and it would be a C3 or comment.
If the single is surface fixed or in an area likely to abrasion / impact then a recommendation would be to replace that cable with an earthed variety.
If there is a 30mA RCD in place then this would also reduce the risk of shock.
 
As a design now it is not a good arrangement (and would be difficult to arrange).
I would assume this is in relation to two wire two way switching of lighting where singles have been used to supply the switch and feed the light.
If the single core is adequately protected from mechanical damage and has been in place for a long time then there should be no significant risk and it would be a C3 or comment.
If the single is surface fixed or in an area likely to abrasion / impact then a recommendation would be to replace that cable with an earthed variety.
If there is a 30mA RCD in place then this would also reduce the risk of shock.
Or you could use single insulated and sheathed, with an earth core, you used to be able to get it, not sure about now though,
 
Or you could use single insulated and sheathed, with an earth core, you used to be able to get it, not sure about now though,
You can but is rarely stocked, normally have to order it, reference code is 6241Y. As for the OP if all points are earthed where they need an earth I wouldn't worry about it.
 
Thanks chaps,

Pretty much as i thought with the general views towards a C3. And yes these cables are existing in a domestic dwelling, have mechanical protection, switch boxes earthed by other cables and an rcd covering the lot. One would be unlikely to wire like this these days.

Thanks
 
A few points:

Insulated and sheathed singles are readily available here.

There is no requirement for every cable to have a cpc - only that a cpc be terminated at every point of the wiring. (Otherwise singles would be unusable.)

No code is warranted or permitted as there is no non-compliance with BS7671.
 
After all, appliances can have flexible cables without a cpc and they're more likely to become damaged than fixed wiring. Plus, of course, meter tails don't have a cpc.

However, Appliance cable atleast has a neutral so is 'likely' to trip / blow a fuse if damaged / cut. I'll grant you though that this whole debate is pretty grey and fundamentally also hinging on luck or bad luck of how you catch or damage the cable....

Hey ho....
 
No Code required, you have stated what needs earthing is earthed. Unless these separately run cpcs are unenclosed and below 4.0mm csa.
 

Reply to Double insulated singles on 2 way switching in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
I have a fairly typical setup of the light on my landing being able to be controlled by both a switch on the landing and a switch at the bottom of...
Replies
1
Views
2K
Looking for some advice; I am intending to mount two led downlights on pillars/brick walls either side of the garage door opening. I will drill...
Replies
4
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock