Discuss Earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Morning all. So just trying to refresh my grey matter but having a biff moment. Earth fault loop impedance with circuits protected by BS EN60898 type B circuit breakers. I know the tabulated values are in table 41.3, but for the life of me I’ve forgotten how to calculate if acceptable or not. So for example; 40A circuit breaker, measured Zs 0.5, maximum tabulated value 1.09. How do I get the corrected values and see if acceptable? Any help for my non firing brain would be greatly appreciated. TIA.
 
As in multiply the tabulated by 0.8 to account for increased resistance on the cable under load conditions?
 
The values in table 41.3 BS7671 need to be multiplied as above (0.8), the values within the on site guide have already been adjusted to reflect the 0.8
 
and don't forget Cmin. that takes another 5% off the max. allowed value. however. I'm skeptical about the 0.8 correction esp. in a domestic. the 0.8 assumes that cables will be running @ 70 deg.C. that is loaded to the max. If you go with the design current Ib, rare you'll see cables getting that warm, only on things like showers.
 

Reply to Earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
583
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock