EICR or Minor Works???

Discuss EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Just a quick one.. I have been to a job today where the shower isolator switch had burnt out, as it wasn't RCD protected I replaced the switch with a 1 way consumer unit with an RCD.

My question is..do I need to do a full EIC or would a minor works do?

Cheers
 
Last edited:
Why did you not fit an RCD in an enclosure the circuit should already have a protective device at the circuit origin so from that perspective I can see why members are saying EIC as a new circuit. I assume this existing burnt out switch was either outside the bathroom or in an adj cupboard. I agree with Pete on what is wrong with adding an RCD to increase the level of safety. It's MW but there would be nothing wrong with issuing an EIC just more paperwork.
 
You haven't wired a new circuit, you have altered an existing circuit MNW
I could kind of see where ESSEX was sort of coming from as switchgear rather than an accessory a subdistribution circuit has been made hence why saying EIC if an RCD in an enclosure replaced the isolation switch it would have been a straight MW.Still agree though can be MW for what's done.
 

Reply to EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock